ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
jraef 4
Recent Posts
Dryer, Range grounding from "Main" panel
by sparkync. 05/25/17 05:49 PM
210.70 / Wall Switch / When adopted?
by gfretwell. 05/24/17 09:18 PM
Any UL 508 experts out there?
by sparkyinak. 05/23/17 11:04 PM
Heat pump conundrum
by sparkyinak. 05/21/17 08:49 PM
Interesting week
by HotLine1. 05/20/17 11:57 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,775 Are you busy
171,793 Re: Forum
164,722 Need opinion
Who's Online Now
0 registered members (), 60 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#200191 - 03/24/11 01:46 PM 12/3 feeder to garage  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 819
NC
Tell me if I'm right:
If I run 12/3 UF cable to a detached garage to feed lights and receptacles I would not have to drive a ground rod at the detached building??? I know to put a double pole breaker on the multi/wire circuit. Also will I have to provide another means of disconnect at the garage for the circuits??
I'm not planning on doing it like this, but just in case the customer wants to go the cheapest route, I want to make sure. Thanks for the input


2017 / 2014 NEC & Related Books and Study Guides

#200196 - 03/24/11 03:40 PM Re: 12/3 feeder to garage [Re: sparkync]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
Just don't call it a feeder, it is a "single branch circuit" and put the breaker on the line end, in the house. Then you get the exceptions.
You still need a disconnect but that can be a 2 pole snap switch or two single poles marked "disconnect". The switches have to be rated at the load and 15a or greater.
Personally I would use a 2 pole 30a to make everyone happy.
(Ref 225.30-225.39)


Greg Fretwell

#200197 - 03/24/11 03:41 PM Re: 12/3 feeder to garage [Re: sparkync]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,826
Brick, NJ USA
2008 NEC 250.32(A) exception:

Exception: A grounding electrode shall not be required where only a single branch circuit, including a multiwire branch circuit, supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the normally non–current-carrying metal parts of equipment.



John

#200201 - 03/24/11 06:41 PM Re: 12/3 feeder to garage [Re: HotLine1]  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 819
NC
Thanks for the replies. That's what I was thinking but just didn't have the code reference available. Greg, would it not still be considered a "branch circuit" even if I did come out of the outside panel, as long as the outside panel has a "main breaker" in it?? Thanks again.


#200203 - 03/24/11 10:08 PM Re: 12/3 feeder to garage [Re: sparkync]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
As long as it is on the load side of the last over current device it is a branch circuit.


Greg Fretwell


Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.002s) Memory: 0.7690 MB (Peak: 0.9114 MB) Zlib enabled. Server Time: 2017-05-25 23:50:57 UTC