#199054 - 02/11/11 11:51 PM Readily available (Ha Ha) AFCI Receptacle!  
PAteenlectrician  Offline
Member
Joined: Jan 2011
Posts: 64
Cressona, Pa, U.S.A. (Schuylki...
When will the AFCI receptacles be available?


2017 / 2014 NEC & Related Books and Study Guides

#199088 - 02/13/11 02:04 AM Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician]  
PAteenlectrician  Offline
Member
Joined: Jan 2011
Posts: 64
Cressona, Pa, U.S.A. (Schuylki...
Your utter silence tells me you don't know.


#199093 - 02/13/11 12:52 PM Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
PAteen:

There are quite a few threads on the elusive AFCI device in the forum.

The 'latest sighting' was within the 2011 NEC Changes book(s), again showing the 'prototype' device from P&S Legrand. My person info on this is from a P&S rep; "not available!"

End of story!


John

#199094 - 02/13/11 02:40 PM Re: Readily available (Ha Ha) AFCI Receptacle! [Re: HotLine1]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
AFAIK, they are still not currently available and since they arenít required for replacement purposes until 2014, my guess is that manufactures are probably not in any rush to produce them.


#199114 - 02/13/11 11:03 PM Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician]  
PAteenlectrician  Offline
Member
Joined: Jan 2011
Posts: 64
Cressona, Pa, U.S.A. (Schuylki...
I wish they are available now, for even more safety in my extension cords. My house is wired with romex, so I cannot use them there.


#199115 - 02/13/11 11:49 PM Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician]  
crselectric  Offline
Member
Joined: Sep 2006
Posts: 133
albany, ca
why would you not be able to use them on romex?? confused


#199116 - 02/14/11 12:06 AM Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
210.12 Exception No. 1: Where RMC, IMC, EMT or steel armored cable, Type AC, meeting the requirements of 250.118 using metal outlet and junction boxes is installed for the portion of the branch circuit between the branch-circuit overcurrent device and the first outlet, it shall be permitted to install a combination AFCI at the first outlet to provide protection for the remaining portion of the branch circuit.


Greg Fretwell

#199123 - 02/14/11 11:50 AM Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician]  
ghost307  Offline
Member
Joined: May 2005
Posts: 916
Chicago Illinois USA
I was told by one of the manufacturers that they realize that they'd sell a ton of them in Chicago, where metallic conduit is required for just about everything; but that they doubt that starting up a product with only 1 local market makes any economic sense.

And if Chicago ever drops that requirement...there would be zero buyers anymore.

Something tells me that these will not be available...at least not from any of the usual reputable manufacturers.


Ghost307

#199126 - 02/14/11 01:17 PM Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician]  
PAteenlectrician  Offline
Member
Joined: Jan 2011
Posts: 64
Cressona, Pa, U.S.A. (Schuylki...
I can see it being used. Not too often, though.


#199127 - 02/14/11 01:32 PM Re: Readily available (Ha Ha) AFCI Receptacle! [Re: PAteenlectrician]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
HUH?

As I see it , the real advantage is for use in replacing existing receptacles in existing construction. I believe it is the intent to require such a receptacle to be used in repairs to non-AFCI-protected circuits after the next code cycle.

(Guess that means they'll want them to be tamper-resistant as well. Can this possible become more of a cluster-flock than it already is?)

Likewise, the 'first receptacle' business allows us to add AFCI protection to an old home that has a fuse box or obsolete panel. Since the expressed purpose of these gizmos is to prevent fires from frayed wiring, it seems logical that it's the OLD homes that need them the most.

There's a certain amount of BS in the distribution chain. When AFCI's were first introduced, Leviton was swearing, and the UL plant inspector verified, that they had pallets of these things in the warehouse. Yet, Graybar was telling me that they were 'not available.' I ran into a similar issue with CED. Only several months after the AFCI requirement was locally adopted did the things suddenly become 'available.'

It's not the only item where the supply house, and the manufacturer, had differing views. Heck, I've often encountered different views between the manufacturers and their own advertising. Sometimes I'm amazed that anything ever reaches the intended user!


Page 1 of 2 1 2

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 17 (0.004s) Memory: 0.8194 MB (Peak: 1.0019 MB) Zlib enabled. Server Time: 2017-10-20 23:03:28 UTC