ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
300 watt transformer
by gfretwell. 10/23/17 10:21 PM
VFD MotorFeeders
by Yoopersup. 10/22/17 07:52 PM
Generator Cable Sizing
by brsele. 10/18/17 07:39 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,471 Are you busy
177,477 Re: Forum
169,037 Need opinion
Who's Online Now
0 registered members (), 13 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#198336 - 01/18/11 11:41 PM lightning protection conductor  
triple  Offline
Member
Joined: Apr 2002
Posts: 184
Wisconsin
The lightning protection wire is run inside pvc through the building I am working on. However, a 50' stretch is run outside the pvc and simply strapped-up to the steel decking through the ceiling of one room. Surely this cannot be allowed? In the event of a lightning strike, couldn't the arcing and sparking created between the wire and the deck result in a fire?


2017 / 2014 NEC & Related Books and Study Guides

#198340 - 01/19/11 01:41 AM Re: lightning protection conductor [Re: triple]  
georgestolz  Offline
Member
Joined: Jun 2005
Posts: 91
Fort Collins, CO, US
I can't think of an NEC violation, but it might run against the... NFPA 780? Whatever the lightning one is.


-George

#198347 - 01/19/11 10:40 AM Re: lightning protection conductor [Re: georgestolz]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Lightning protection here (NJ) are installed by "Certified Installers" to the best of my knowledge. As an EC, the sites that I worked on (Country Clubs) had a lightning contractor.

What you described does not sound 'right', but that's just a off the cuff comment. All the conductors that I have noticed were routed on the exteriors of the structures.



John

#198505 - 01/24/11 02:27 PM Re: lightning protection conductor [Re: HotLine1]  
sabrown  Offline
Member
Joined: Dec 2002
Posts: 302
Ogden, Utah, USA
Just some items to be aware of besides the certified installer.

There is no typical requirement stating that the "down conductors" not allowed being run through the interior of a building. That being said, it does create alot more bonding issues that must be taken care of (flashovers).

There is no normal installation "shall" requirement that the conductors be in conduit.

But simply strapping a down conductor to steel decking does not meet bonding requirements assuming strapping means something to just hold the condutors in place (every 36" maximum). These are typically bonded via bonding plates or cadwelded. Whatever is used it is listed for lightning protection and has very specific requirements.

There are however requirements for regular yearly inspection of the system.

I am sorry that I can't put more information into this reply, but that would involve teaching a course on lightning protection.



Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 15 (0.003s) Memory: 0.7607 MB (Peak: 0.8938 MB) Zlib enabled. Server Time: 2017-10-24 07:51:12 UTC