#198140 - 01/13/11 02:48 PM Underground requirements  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 829
NC
Around here for years when using a trench for burying USE cable in residential areas, it's always said that the requirement was 18", but as I read in the code it's actually 24" unless it's under a residential driveway or parking area. I'm talking about a normal run to a out building from a main panel not running under any concrete or not in conduit. Am I the only one that's been with this assumption? I've think I've even had inspectors tell me 18" before. Any thoughts on this??? Thanks...
Also when driving ground rods for a subpanel in a detached building, I'm under the assumption that it is still (2) ground rods at least 6ft. apart and attached to the grounding bar in the subpanel...???

Last edited by sparkync; 01/13/11 02:50 PM.

2017 / 2014 NEC & Related Books and Study Guides

#198146 - 01/13/11 03:22 PM Re: Underground requirements [Re: sparkync]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,135
Estero,Fl,usa
300.5 says 24" for direct burial cable/conductors unless this is a residential, single circuit, GFCI at the source end, 120v, 20a max, which can be 12"
That loophole also eliminates the need for a ground rod.

Anything else puts you into 225 part II and 250.32 along with the deeper 300.5 requirements.

They put the single residential circuit loophole in there to compromise a safer alternative to running an orange cord through the trees or along the ground.
If digging is hard there, RNC at 18" becomes a very attractive option. Personally I would go that way anyhow.


Greg Fretwell

#198182 - 01/14/11 03:41 AM Re: Underground requirements [Re: sparkync]  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
Originally Posted by sparkync
Also when driving ground rods for a subpanel in a detached building, I'm under the assumption that it is still (2) ground rods at least 6ft. apart and attached to the grounding bar in the subpanel...???


The 6' rule is valid but i don't think you need two ground rods unless the resistance of the one electrode is higher than 25 ohms.


Be kind to your neighbor, he knows where you live



Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.002s) Memory: 0.7527 MB (Peak: 0.8763 MB) Zlib enabled. Server Time: 2017-11-19 10:17:25 UTC