#198101 - 01/12/11 08:24 PM UPS system  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
I have a client who has 3 UPS system with a total 10KVA capacity. They currently have a 30Amp feeder with a Subpanel in the communication room.
They have asked me to install a 60Amp feeder for additional UPS units.

here are the question/s that i have.
>I assume i need to have a disconnect within site of the UPS units? Right?
>I will size the feeders to 125%?
>Existing, the UPS feeds the Existing sub panel by a SOO cord, is that O.K.

Thank you for your input


Be kind to your neighbor, he knows where you live


Work Gear for Electricians and the Trades

#198116 - 01/12/11 11:44 PM Re: UPS system [Re: Niko]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,864
Brick, NJ USA
Niko:

Yes to the disconnect.
125% is OK
Possibly OK, but more info is needed. Is the connection from the UPS via a cord cap? Is there frequent 'swapping' of the UPS? IF yes, then the cord could be acceptable.



John

#198117 - 01/13/11 12:57 AM Re: UPS system [Re: HotLine1]  
Niko  Offline
Member
Joined: Aug 2006
Posts: 356
Campbell, CA
There is no frequent swapping of UPS. Currently the UPS is cord & cap connected to the feeder receptacle sized 6AWG then the UPS feeds the subpanel sized 6AWG cord.





Be kind to your neighbor, he knows where you live



Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.002s) Memory: 0.7516 MB (Peak: 0.8796 MB) Zlib enabled. Server Time: 2017-09-26 00:18:35 UTC