#197091 - 11/08/10 12:10 PM 210.52[E],3  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Looking over 210.52[E],3 which requires at least one receptacle outlet for balconies, decks and porches of any size, it says the it shall be located not more than 6-1/2 feet above the surface of that area.
So, if this were a GFCI receptacle, would this mean that this is also the maximum height which will meet the readily accessible requirement of 210.8?


2017 / 2014 NEC & Related Books and Study Guides

#197093 - 11/08/10 02:57 PM Re: 210.52[E],3 [Re: KJay]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,874
Brick, NJ USA
Kjay:
As I believe the 'change' was to include any size balcony, porch, etc. and the balance of this section remains the same as '08, I would have to say this GFI receptacle would be acceptable at 6'6" max and be readily accessable.



John

#197108 - 11/09/10 12:08 AM Re: 210.52[E],3 [Re: HotLine1]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Yes, I see that they took out the square footage and now made it mandatory for all, regardless of size.

So I guess unofficially anyway, it sounds like a GFCI device can be mounted up to 6-1/2 feet high and anywhere between 0-inches to infinity as far as distance is concerned and still meet the definition of readily accessible.


#197111 - 11/09/10 09:39 AM Re: 210.52[E],3 [Re: KJay]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,874
Brick, NJ USA
Interesting thought....

Using the defacto info that a receptacle 5 1/2' high or over does not count for resi spacing, and the supposition that utilization equipment cords are 6' from mfg, the 61/2' height would raise concerns. An invitation for extension cords perhaps?

Basically, my point is place a floor lamp with a 6' cord on the balcony, and you cannot plug it in without an extension cord.

Make any logical sense??



John


Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.002s) Memory: 0.7601 MB (Peak: 0.8934 MB) Zlib enabled. Server Time: 2017-11-18 13:46:02 UTC