ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 3
Recent Posts
Nec circuit protection
by Yoopersup. 11/22/17 03:22 PM
FPE in Germany
by Texas_Ranger. 11/19/17 07:30 AM
Ceiling fan distance from outdoor hot tub
by gfretwell. 11/16/17 02:18 AM
diazed fuses
by Texas_Ranger. 11/13/17 03:02 PM
Theft deterrent alarm
by gfretwell. 11/12/17 01:39 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
242,659 Are you busy
178,871 Re: Forum
170,085 Need opinion
Who's Online Now
0 registered members (), 11 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#196917 - 11/01/10 06:02 PM Re: Knockouts  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Are you allowed to use a bonding locknuts with concentric/eccentric knockouts?

P.S. Greg, you know where I am going with this, let's see what others have to say.


Work Gear for Electricians and the Trades

#196919 - 11/01/10 06:09 PM Re: Knockouts [Re: harold endean]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
I gave you my cite, lets see what everyone else has to say.


Greg Fretwell

#196931 - 11/01/10 09:26 PM Re: Knockouts [Re: harold endean]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
UL White Book seems to indicate no problem for metal outlet boxes, regardless of voltage, but then 250.97 doesn’t specifically list them as one the methods in the exceptions for bonding over 250V.


#197010 - 11/04/10 11:06 PM Re: Knockouts [Re: KJay]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Raco junction boxes are rated/listed for use with 277V circuits even with concentrics.

Ditto the competition, IIRC.

The only time I face issues is with disconnects -- especially NEMA3R for RTU.

I've never been given the opportunity to install bonding locknuts. Out my way, the only ones I've seen are in Code Handbooks.

-----------

I can say from witnessing aged rooftop installations that bonding takes a beating over time. Hence, I always run a separate bonding conductor for all circuits that leave the building.

If you've never seen it, what happens to roof top EMT runs is trips and falls. Over the years various HVAC boys manage to bump what ever EMT can possibly be bumped.

As for current installations, root top EMT runs are either contract prohibited or banned by the AHJ. Only short, to the point, EMT is permitted.

BTW, old disconnects/fuse holders are scary. Generally they are too small and too often they do not keep rain or leaves out. And then the labels are all ruined. This is not the type of stuff to handle on a wet roof.



Tesla

#197014 - 11/05/10 08:48 AM Re: Knockouts [Re: Tesla]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
The situation I am writing about deals with a new panel installed before that main service breaker. It feeds a PV system. So the feeder to this new PV panel has no overcurrent protection. Now Would a bonding locknut be suitable for use on a panel with concentric knockouts?


#197016 - 11/05/10 12:31 PM Re: Knockouts [Re: harold endean]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
Harold I have modified my position. I am thinking it will be acceptable. The function of the bonding locknut is to bond the raceway and if it is made up tight against the connector lip and the concentric ring with a 250.66 sized jumper, the raceway is bonded, even if the ring breaks out completely.

For some reason I had in it my mind that the concentric locknut would loosen if the eccentric broke. I guess I should not type after midnight wink


Greg Fretwell

#197020 - 11/05/10 12:57 PM Re: Knockouts [Re: gfretwell]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,

If the concentric KO pops out, the grounding would be lost. The bonded locknut will still be tight against the shoulder of the connector, but the metal to metal grounding will be missing because the KO busted loose. Right?


#197021 - 11/05/10 01:15 PM Re: Knockouts [Re: harold endean]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,136
Estero,Fl,usa
Not if there is a jumper from the locknut to the can.


Greg Fretwell

#197028 - 11/05/10 07:33 PM Re: Knockouts [Re: gfretwell]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
BTW, it is important to acknowledge that PV systems -- as generators of power are NOT infinite busses.

Further, solid-state current saturation effects mean that the kind of peak arc power available from an infinite bus does not exist.

This is true whether you're on the DC or AC side of the inverter.



Tesla

#197031 - 11/05/10 08:44 PM Re: Knockouts [Re: Tesla]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
I thought bonding locknuts just had a screw that you tighten against the box after tightening them down. If it has lug with a bonding jumper attached, wouldn’t that be a bonding bushing?


Page 1 of 2 1 2

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 16 (0.003s) Memory: 0.8175 MB (Peak: 0.9994 MB) Zlib enabled. Server Time: 2017-11-24 07:16:31 UTC