#196870 - 10/30/10 03:41 AM Future less restrictive code trumps present code?  
Yeknom  Offline
New Member
Joined: Aug 2006
Posts: 7
New York, NY, Manhattan
If a condition is permitted under the 2008 NEC, but violates the 2005 NEC will it nevertheless be issued a violation, by a municipality that has not yet adopted the 2008 code and is still operating under the 2005 Code? (NYC).
(Specifically I am concerned with 690.64(B)(2) which is LESS RESTRICTIVE in 2008 than in 2005.

Will that violation in general automatically be removed (voided, nullified) when the city adopts the 2008 code?


2017 / 2014 NEC & Related Books and Study Guides

#196872 - 10/30/10 11:35 AM Re: Future less restrictive code trumps present code? [Re: Yeknom]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,874
Brick, NJ USA
Yekmon:
On this side of the river (NJ) the 'codes' that are in effect upon issuance of the project permit prevail to the closure of that job.

However, a 'variation' could be applied for tho the AHJ for consideration. Variations are not granted for life-safety, or ADA compliance.


John

#196873 - 10/30/10 11:48 AM Re: Future less restrictive code trumps present code? [Re: HotLine1]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,135
Estero,Fl,usa
In Florida they passed an addendum to the building code to soften the "paved surface" bonding rules to reflect the 2008 changes(680.26(B)(2)(b)(1)), before we adopted the 2008. It is really the only legal way to do it if you are not using 90-4.


Greg Fretwell

#196875 - 10/30/10 11:53 AM Re: Future less restrictive code trumps present code? [Re: Yeknom]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
I would say yes.
That reminds me of a similar reverse situation where SE cables installed inside buildings under the '08 code were limited to 60-degree C, like NM cables, but might now be rated up to 75-degree C under the 2011.
That is, if this change was actually made. I dont have the 2011 NEC yet to verify this though


#196876 - 10/30/10 12:01 PM Re: Future less restrictive code trumps present code? [Re: KJay]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,874
Brick, NJ USA
Kjay:
From the 2011 (PDF version), book is in office...is this what you're looking for...

"(4) Installation Methods for Branch Circuits and Feeders.
(a) Interior Installations. In addition to the provisions
of this article, Type SE service-entrance cable used for interior
wiring shall comply with the installation requirements
of Part II of Article 334, excluding 334.80.
Where installed in thermal insulation, the ampacity shall
be in accordance with the 60C (140F) conductor temperature
rating. The maximum conductor temperature rating
shall be permitted to be used for ampacity adjustment and
correction purposes, if the final derated ampacity does not
exceed that for a 60C (140F) rated conductor.
Informational Note No. 1: See 310.15(A)(3) for temperature
limitation of conductors.
Informational Note No. 2: For the installation of main
power feeder conductors in dwelling units refer to
310.15(B)(7).
(b) Exterior Installations. In addition to the provisions
of this article, service-entrance cable used for feeders or
branch circuits, where installed as exterior wiring, shall be
installed in accordance with Part I of Article 225. The cable
shall be supported in accordance with 334.30. Type USE
cable installed as underground feeder and branch circuit
cable shall comply with Part II of Article 340.
338.12 Uses Not Permitted.
(A) Service-Entrance Cable. Service-entrance cable (SE)
shall not be used under the following conditions or in the
following locations:
(1) Where subject to physical damage unless protected in
accordance with 230.50(B)
(2) Underground with or without a raceway
(3) For exterior branch circuits and feeder wiring unless
the installation complies with the provisions of Part I of
Article 225 and is supported in accordance with 334.30
or is used as messenger-supported wiring as permitted
in Part II of Article 396
(B) Underground Service-Entrance Cable. Underground
service-entrance cable (USE) shall not be used under the
following conditions or in the following locations:
(1) For interior wiring
336.116 ARTICLE 338 SERVICE-ENTRANCE CABLE: TYPES SE AND USE
70200


John

#196877 - 10/30/10 12:20 PM Re: Future less restrictive code trumps present code? [Re: HotLine1]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
It doesnt appear that they made any real change to this.
Oh well, at least MA allows it to be used at 75-degree C under certain conditions, with the 08 code anyway.


#196879 - 10/30/10 01:05 PM Re: Future less restrictive code trumps present code? [Re: KJay]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Lovely little conundrum, isn't it? Maybe we need to keep that in mind when we try to 'perfect' codes, or get into design issues. It's also a caution about blindly accepting whatever the 'wiseguys' decide.

Yet, with a newer 'model' code published, but not adopted, it is simply wrong to enforce language that has since been removed. That's precisely the sort of thing that led to the creation of the jury system - where no one is bound by 'precedent' or 'logic.' Indeed, the jury is the one place where someone can refuse to enforce a law that is seen as simply wrong, or wrongfully applied.

It's no accident that the Soviet author and political prisoner Alexander Solzhenitsyn wrote of several such instances: folks imprisoned for making 'treasonous' or 'antisocial' assertions that were later found to be accurate. Unfortunately, that did not often result in the convicted being released. Nor was the 'system' in any way self-correction; the convict had to petition for a review.

We can't 'petition for review' after a building is built. Once an expensive error is made, the money and time is gone forever. So what's the solution?

Well, I've seen town councils move with lightning speed to enact bans on whatever harmless behavior becomes popular with unpopular ethnic, religious, or age groups. I suggest every inspector get the wheels turning to have enforcement of these questionable code provisions officially be put on hold, as quickly as possible.


#196881 - 10/30/10 04:29 PM Re: Future less restrictive code trumps present code? [Re: renosteinke]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,135
Estero,Fl,usa
Unfortunately code is either adopted as written, modified or not adopted. You can't cherry pick rules from unadopted codes.
We are enforcing laws here and they have to be the law as written.


Greg Fretwell

#196882 - 10/30/10 05:10 PM Re: Future less restrictive code trumps present code? [Re: gfretwell]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
That is simply not true. All it takes is for the city council to adopt an ordinance, and the ordinance can say whatever you want. I've yet to see a city department that didn't know exactly how to get something voted on at the next board meeting; in the meantime, there's usually a machanism to issue a temporary order until the next meeting.

As for simply enforcing laws as written - the 'just following orders' canard was dethroned decades ago.

Of course, I'm assuming that the town is the AHJ. Where that's not the case .... well, there seems to have been plenty of places that found ways to not comply with various laws to which they disagree. San Francisco's been pretty prominent, for example, in declaring that no city office will do anything to comply with (or enforce) immigration laws.

Simply put, where there's a will there's a way.

Of course I would prefer that this issue not arise. Let's think about that the next time we feel the need to add pages to the code books.


#196894 - 10/31/10 12:59 PM Re: Future less restrictive code trumps present code? [Re: renosteinke]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,135
Estero,Fl,usa
If the city, having jurisdiction, writes an ordinance, the code, as adopted, was "modified" then wasn't it?
The fact remains, until the new code is adopted or until the old code is modified, the code that was adopted is still law.


Greg Fretwell

Page 1 of 2 1 2

Member Spotlight
akmaster
akmaster
alaska
Posts: 70
Joined: June 2012
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.041s Queries: 16 (0.021s) Memory: 0.8235 MB (Peak: 1.0067 MB) Zlib enabled. Server Time: 2017-11-19 16:15:07 UTC