3 wire circuits #196798
10/27/10 07:21 PM
10/27/10 07:21 PM
dougwells  Offline
OP
Member
Joined: May 2003
Posts: 1,142
kamloops BC Canada
I had a customer call today, he was wondering if his main panel could be moved as it was in a basement suite kitchen. on the wall behind the cooktop stove and counter.

Anyhow when I looked in the panel someone had loaded it up with tandem breakers on 3 wire circuits. I think some of these circuits are split appliance circuits and they took out the double pole breakers and installed tandems to free up spaces.

A home inspector had took off the panel cover and told the buyer everything was fine.

I am sure the use of the tandem QO breakers on a 3 wire circuit (mwbc) is a violation am I right ??

Tools for Electricians:
Re: 3 wire circuits [Re: dougwells] #196800
10/27/10 08:55 PM
10/27/10 08:55 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,917
Brick, NJ USA
Doug:
This side of the border, you are 100% right. Guess some of our HIs moved up to you?



John
Re: 3 wire circuits [Re: HotLine1] #196801
10/27/10 09:46 PM
10/27/10 09:46 PM
dougwells  Offline
OP
Member
Joined: May 2003
Posts: 1,142
kamloops BC Canada
I would say there was at least 8 tandem breakers with reds and blacks on them. doubled up neutrals landed under each screw on the neutral strip also.

It was tesla that actually made me aware to look for this when i saw the tandems

https://www.electrical-contractor.n...l_to_find_open_neutral_i.html#Post196375

Re: 3 wire circuits [Re: dougwells] #196808
10/28/10 09:35 AM
10/28/10 09:35 AM
J
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
If the 3 wrie circuits have both side on the same leg it is definitely a violation. If he still managed to keep the phasing correct on the circuits it could be fine. Only circuits where both legs land on the same device(split wired receptacle) are handle ties/double pole breakers required.

Re: 3 wire circuits [Re: jdevlin] #196810
10/28/10 11:52 AM
10/28/10 11:52 AM
dougwells  Offline
OP
Member
Joined: May 2003
Posts: 1,142
kamloops BC Canada
Originally Posted by jdevlin
If the 3 wrie circuits have both side on the same leg it is definitely a violation. If he still managed to keep the phasing correct on the circuits it could be fine. Only circuits where both legs land on the same device(split wired receptacle) are handle ties/double pole breakers required.


humm I thought all multiwire branch circuits required a 2 pole breaker mainly because the neutral would still be energized

Re: 3 wire circuits [Re: dougwells] #196811
10/28/10 12:03 PM
10/28/10 12:03 PM
G
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
The handle tie/ two pole breaker question depends on which code cycle was in effect when the work was done. Current 2008 code cycle calls for ALL multiwire branch circuits to be simultaneously disconnectable, not just those on a common yoke. MWBC's terminated on the same phase sharing a common neutral would be a violation if the neutral is not oversized, something that just doesn't happen in resi construction.

Re: 3 wire circuits [Re: Gregtaylor] #196814
10/28/10 03:04 PM
10/28/10 03:04 PM
J
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
This is direct from ESA last month. Please note this is the CANADIAN code forum. Rules are different in NEC world.

Quote
If wiring a dedicated circuit can 1/2 of a multiwire circuit be used as a dedicated circuit.

Example can a 14/3 be pulled to the fridge receptacle and black and white for fridge and then red and white used for lighting?

Is a double pole breaker required or can two singles be used if proper installed on opposite legs of the service?


--- (yousefr) 9/16/2010 9:48:36 AM
1. Each side of a 3-wire circuit can be considered as a separate dedicated circuit if they are properly connected to different phases and have common neutral.

2. Yes, a double pole breaker or two singles can be used (if properly installed on opposite legs of the service) for a 3-wire circuit.

Reference is to the Ontario Electrical Safety Code 24th Edition/2009.



Ray Yousef
Assistant Code Engineer

Last edited by jdevlin; 10/28/10 03:06 PM.
Re: 3 wire circuits [Re: jdevlin] #196815
10/28/10 05:48 PM
10/28/10 05:48 PM
dougwells  Offline
OP
Member
Joined: May 2003
Posts: 1,142
kamloops BC Canada
Thanks
jdevlin

Re: 3 wire circuits [Re: dougwells] #196817
10/28/10 06:54 PM
10/28/10 06:54 PM
G
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
I didn't see that this was a Canadian code question before I answered. Sorry.

Re: 3 wire circuits [Re: dougwells] #196818
10/28/10 06:55 PM
10/28/10 06:55 PM
M
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
The term Tandem can cause some confusion. There was a tandem breaker that used 1 pole from the bus and had 2 15 amp ccts available. This breaker would not be appropriate for a shared neutral unless the neutral was good for 30 amps and even then would still not be code compliant. there are also side by side mini breakers that also used a single pole off the buss. Again this would not allow a common neutral.
To share a neutral whether for 2 circuits from a 3 wire or a split receptacle both current carrying poles must come from a different phase so the voltage between poles is 240 volts and not 0 volts, In both cases there would be 120 volts to ground or neutral.
In the case of a split plug a 2 pole common trip breaker or tie bar is required.
A 3 wire circuit supplying 2 different loads and not on a receptacle with a common yolk can use 2 1 pole breakers on adjacent phases without requiring a tie bar.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
sparky 22
Admin 20
Potseal 13
Popular Topics(Views)
243,530 Are you busy
180,332 Re: Forum
170,823 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.033s Queries: 16 (0.005s) Memory: 1.0257 MB (Peak: 1.2033 MB) Zlib enabled. Server Time: 2018-01-18 04:04:27 UTC