#196763 - 10/26/10 09:16 PM bath vent fan proximity protection needed?  
crselectric  Offline
Member
Joined: Sep 2006
Posts: 133
albany, ca
Having trouble locating rule,one of those afternoons, Is it three feet from bath or shower, to require gfi prot.?
Chris


Work Gear for Electricians and the Trades

#196767 - 10/26/10 09:50 PM Re: bath vent fan proximity protection needed? [Re: crselectric]  
crselectric  Offline
Member
Joined: Sep 2006
Posts: 133
albany, ca
three feet comes to mind, but I can't find in code?


#196768 - 10/26/10 09:52 PM Re: bath vent fan proximity protection needed? [Re: crselectric]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
The fan manufacturer’s instructions for the ones I use usually only require GFCI for them when they are directly in or over the tub or shower itself.
A paddle fan would be a different story. Check out NEC 410.10[D] anyway.
Do you have other local requirement for this?


#196770 - 10/26/10 10:48 PM Re: bath vent fan proximity protection needed? [Re: KJay]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,122
Estero,Fl,usa
KJay is right, 410.10(D) is where the 3 feet comes from but that is a paddle fan.

Quote
(D) Bathtub and Shower Areas. No parts of cord-connected luminaires, chain-, cable-, or cord-suspended luminaires, lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold. This zone is all encompassing and includes the space directly over the tub or shower stall. Luminaires located within the actual outside dimension of the bathtub or shower to a height of 2.5 m (8 ft) vertically from the top of the bathtub rim or shower threshold shall be marked for damp locations, or marked for wet locations where subject to shower spray.


Greg Fretwell


Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 810
Joined: April 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.004s) Memory: 0.7597 MB (Peak: 0.8911 MB) Zlib enabled. Server Time: 2017-10-18 21:58:41 UTC