ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 3
dsk 3
Recent Posts
Feed to spa panel
by HotLine1. 06/25/17 05:28 PM
Weatherhead, POA, height?
by HotLine1. 06/24/17 02:37 PM
Windows 7 update problem
by ampherder. 06/21/17 07:01 AM
Norwegian power?
by dsk. 06/19/17 03:40 PM
Anyone ever take a Furnas A14D drum sw apart?
by gfretwell. 06/17/17 08:14 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
238,245 Are you busy
173,462 Re: Forum
166,264 Need opinion
Who's Online Now
0 registered members (), 59 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#195737 - 08/20/10 12:28 AM underwater lights  
schenimann  Offline
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
I am repairing some underwater lights in a pond. They are line voltage and are from the Roman lighting company. They are sealed lights that come with a whip attached. They mount with a set screw on a post and shine up on a sign under a waterfall.

This is new ground for me. Is it required that they be gfci protected? According to 680.23(3) they need to be protected during relamping. They cannot be energized when they are out of the water and cannot be relamped when under water.



Work Gear for Electricians and the Trades

#195738 - 08/20/10 02:38 AM Re: underwater lights [Re: schenimann]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
Is this a natural waterfall or pumped water?
If it is pumped water you have a fountain and 680.51 applies

Quote
680.51 Luminaires, Submersible Pumps, and Other Submersible Equipment.

(A) Ground-Fault Circuit Interrupter. Luminaires, submersible pumps, and other submersible equipment, unless listed for operation at 15 volts or less and supplied by a transformer that complies with 680.23(A)(2), shall be protected by a ground-fault circuit interrupter.


If this is a natural pond and waterfall, it is not clear you need a GFCI for an underwater light, only a receptacle. See article 682



Greg Fretwell

#195742 - 08/20/10 09:22 AM Re: underwater lights [Re: gfretwell]  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Greg,

I myself would try to install the lights on a GFI just to err on the side of safety. However that is just my 2 cents. smile


#195753 - 08/20/10 12:24 PM Re: underwater lights [Re: harold endean]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
I agree, anything outside should be GFCI IMHO but there are still some holes in NFPA70.


Greg Fretwell

#195766 - 08/20/10 08:21 PM Re: underwater lights [Re: gfretwell]  
schenimann  Offline
Member
Joined: Feb 2008
Posts: 193
Western North Carolina
I didi the repair today. The original install was three circuits, each to a double gang weather box at the pond. They had put a gfci dead front in the box with a blank cover over it, then caulked the dickens out of it. This was ok until the gfci tripped. I was an easy fix. I put in use covers on the boxes.

I tried gfci breakers. That seemed to be the best set-up, however they wouldn't hold.


#195767 - 08/20/10 09:09 PM Re: underwater lights [Re: schenimann]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,833
Brick, NJ USA
Hmmmmm....

"I tried gfci breakers. That seemed to be the best set-up, however they wouldn't hold."

Wonder why?



John

#195770 - 08/20/10 11:23 PM Re: underwater lights [Re: HotLine1]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,085
Estero,Fl,usa
I imagine the cable/raceway to the pond is damaged or a J box along the way is wet.


Greg Fretwell

#195772 - 08/21/10 12:38 AM Re: underwater lights [Re: gfretwell]  
homer  Offline
Member
Joined: Sep 2004
Posts: 68
Vancouver, WA, USA
It is very common for long runs to trip GFCI devices even when there is no damage to the wiring. The capacitive effect of the conductors running adjacent to each other plus the inrush of the load is often more than enough to cause nuisance tripping. The closer the GFCI is to the load, the less nuisance tripping.

Another possibility is if the wiring shares a conduit or is closely spaced with other circuits (not in conduits) when leaving the panelboard (even for a short distance), the breaker can be more sensitive due to coupling between adjacent circuit wiring, especially if there is high frequency noise generated by computer and/or solid state ballast loads.

Any type of inductive load such as magnetic ballasts or small motors at a distance from the GFCI device will also cause tripping.

This type of nuisance tripping has largely been ignored by the manufacturers. The testing they do is primarily at their labs and they are not out in service trucks, so they don't see a problem.



Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,429
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 15 (0.003s) Memory: 0.7946 MB (Peak: 0.9584 MB) Zlib enabled. Server Time: 2017-06-26 22:35:55 UTC