ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Shout Box
Recent Posts
Video: Inventor of the GFCI self-testing shocks
by Bill Addiss. 01/17/18 11:11 PM
FPE in Germany
by HotLine1. 01/17/18 07:07 PM
VDE 0100 to introduce AFCIs
by LongRunner. 01/17/18 10:32 AM
Fujifilm Recalls Power Adapter Wall Plugs
by Admin. 01/16/18 07:04 PM
Air Compressor feeder conductor sizing
by Potseal. 01/15/18 09:08 PM
New in the Gallery:
Housebilding DIY wiring
SE cable question
Who's Online Now
0 registered members (), 61 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
use branch circuit #194707
06/16/10 03:26 PM
06/16/10 03:26 PM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
I have a wellhead 320 feet from pump house, I am using USE #4 aluminum in a trench not in a raceway...should I tape the wires every 20 feet or so to ensure the cancelling effect or isn't this an issue?
Thanks, H20

Last edited by watersparkfalls; 06/16/10 03:26 PM.
2017 / 2014 NEC & Related Books and Study Guides
Re: use branch circuit [Re: watersparkfalls] #194710
06/16/10 05:02 PM
06/16/10 05:02 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 840
Michigan
300.3 (B) I don;t think the taping is a requirement.

Re: use branch circuit [Re: watersparkfalls] #194711
06/16/10 05:14 PM
06/16/10 05:14 PM
K
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Isn't the USE a triplex assembly or something similar that is already factory twisted?
If not, I can't say that I've ever pulled individual USE conductors before, but I think the twisting is more so that it can be considered a cable assembly and for installation convenience.
Years ago, where I worked at the time, it was common to direct bury individual service conductors and we never had any issues with not twisting the conductors in the trenches, although we did basically lay them right on top of one another anyway.
I couldn't see where it would hurt to twist them though if you wanted.

Re: use branch circuit [Re: KJay] #194717
06/16/10 11:00 PM
06/16/10 11:00 PM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
Thanks, KJ and Yoop. They are single strands of AL USE wire.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 20
Potseal 13
Popular Topics(Views)
243,539 Are you busy
180,341 Re: Forum
170,831 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.024s Queries: 15 (0.004s) Memory: 0.9580 MB (Peak: 1.0906 MB) Zlib enabled. Server Time: 2018-01-18 21:38:47 UTC