#194176 - 05/14/10 02:01 AM Laundry room panel calculation  
Kuzn  Offline
New Member
Joined: May 2010
Posts: 2
BC Canada
Hi I need to calculate the electrical panel capacity for the strata laundry room upgrade. Strata plans to have 3 stacked dryers (dryer/dryer) 240V/60Amp - hardwired and 6 washers 120V/15Amp receptacles. Should I calculate it as 100% continuous load (3*60+6*15) =270 Amp.
Can you please remind me what CEC says?
Thank you


Tools for Electricians:

#194246 - 05/18/10 12:21 PM Re: Laundry room panel calculation [Re: Kuzn]  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
From 8-202 (4) "The ampacity of feeder conductors from a service supplying loads not located in dwelling units shall be not less than the rating of the equipment installed with demand factors as permitted by this code."

So in your case, it is 100%, since you have not listed any electric space heating loads, where you would add them at 75% from 62-116(3).


#194270 - 05/19/10 01:36 PM Re: Laundry room panel calculation [Re: jay8]  
Kuzn  Offline
New Member
Joined: May 2010
Posts: 2
BC Canada
I'm confused with 8-202(3)(d)...power loads not located in dwelling units shell be added with a demand factor of 75%. This panel is for laundry load only, no heating, no lightning.

Thank you


#194272 - 05/19/10 02:56 PM Re: Laundry room panel calculation [Re: Kuzn]  
jay8  Offline
Member
Joined: Jul 2005
Posts: 183
Vancouver, BC
I dont blame you for being confused, but 8-202 (3) refers to the main service feeder calculation while 8-202 (4) refers to just feeders for the house panels.



Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.004s) Memory: 0.7586 MB (Peak: 0.8902 MB) Zlib enabled. Server Time: 2017-10-21 19:32:29 UTC