#193792 - 04/20/10 01:50 AM feeder sizing  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 216
Washington...Not DC
how should I calculate generator feeders? I have a 17 KW generator 71 amps, 310.15 allows #4 for 100 amps, but does it allow #6 for 71 amps? Do I size according to 310.16 which is still #4?
Thanks,
H20


2017 / 2014 NEC & Related Books and Study Guides

#193795 - 04/20/10 03:32 AM Re: feeder sizing [Re: watersparkfalls]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,097
Estero,Fl,usa
You can only use 310.15(B)(6) if this is a main feeder for the entire dwelling, basically an extension of the service entrance from a disconnect. That is, by definition, a #4 minimum. In no case could you interpolate down to a #6.
Any other application has to use 310.16.


Greg Fretwell

#193802 - 04/20/10 12:46 PM Re: feeder sizing [Re: gfretwell]  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 216
Washington...Not DC
thanks Gfretwell



Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.002s) Memory: 0.7515 MB (Peak: 0.8761 MB) Zlib enabled. Server Time: 2017-07-20 16:28:05 UTC