ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 3
Recent Posts
Nec circuit protection
by gfretwell. 11/21/17 11:01 PM
FPE in Germany
by Texas_Ranger. 11/19/17 07:30 AM
Ceiling fan distance from outdoor hot tub
by gfretwell. 11/16/17 02:18 AM
diazed fuses
by Texas_Ranger. 11/13/17 03:02 PM
Theft deterrent alarm
by gfretwell. 11/12/17 01:39 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
242,614 Are you busy
178,812 Re: Forum
170,052 Need opinion
Who's Online Now
0 registered members (), 20 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#193637 - 04/11/10 11:17 PM EGC Bond in Transfer Switch (Code)  
George393  Offline
New Member
Joined: Apr 2010
Posts: 5
AL
A customer requests an addtional circuit (3 outlets) in a stand alone garage.

She has an outside 100 AMP disconnect at the entrance. From there the feeder goes direct to the oposite side of the house and terminates at a Ronk 100 AMP manual transfer switch (for a portable generator hookup).

EGC and all neutrals from the single house distribution panel and the stand alone garage distribution panel are bonded together inside the Ronk manual transfer switch. The house distribution panel and the stand alone garage distribution panel have egc and neutral seperate as required in each panel.

House panel is 125 AMP service. Stand alone garage panel is 100 AMP service.

I cannot find a code section on this.
Q - Can both these two distribution panels be bonded together (EGC and neutral) at the same location inside the Ronk manual transfer switch?
Q - If they can be does the 1st bond of neutral and ground at the outside service entrance disconnect (on the other side of the house) cause a problem by being a second EGC and neutral bond?

Thanks.


2017 / 2014 NEC & Related Books and Study Guides

#193638 - 04/11/10 11:50 PM Re: EGC Bond in Transfer Switch (Code) [Re: George393]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Your code reference is 250.32.

You can not tie the "Grounded" conductor to the equipment after the Service Disconnect. You must carry an equipment ground conductor with any feeders and keep the Grounded conductor (Neutral) and the equipment grounding conductor separated. If your generator is a SDS you must use a 3-pole transfer switch (assume single phase) and transfer the neutral.

By the way Welcome to the forum. With a name like George your okay.


George Little

#193653 - 04/12/10 05:38 PM Re: EGC Bond in Transfer Switch (Code) [Re: George Little]  
George393  Offline
New Member
Joined: Apr 2010
Posts: 5
AL
Thanks George!



Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.002s) Memory: 0.7517 MB (Peak: 0.8749 MB) Zlib enabled. Server Time: 2017-11-22 14:48:55 UTC