#193637 - 04/12/10 12:17 AM EGC Bond in Transfer Switch (Code)  
George393  Offline
New Member
Joined: Apr 2010
Posts: 5
AL
A customer requests an addtional circuit (3 outlets) in a stand alone garage.

She has an outside 100 AMP disconnect at the entrance. From there the feeder goes direct to the oposite side of the house and terminates at a Ronk 100 AMP manual transfer switch (for a portable generator hookup).

EGC and all neutrals from the single house distribution panel and the stand alone garage distribution panel are bonded together inside the Ronk manual transfer switch. The house distribution panel and the stand alone garage distribution panel have egc and neutral seperate as required in each panel.

House panel is 125 AMP service. Stand alone garage panel is 100 AMP service.

I cannot find a code section on this.
Q - Can both these two distribution panels be bonded together (EGC and neutral) at the same location inside the Ronk manual transfer switch?
Q - If they can be does the 1st bond of neutral and ground at the outside service entrance disconnect (on the other side of the house) cause a problem by being a second EGC and neutral bond?

Thanks.


2017 / 2014 NEC & Related Books and Study Guides

#193638 - 04/12/10 12:50 AM Re: EGC Bond in Transfer Switch (Code) [Re: George393]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Your code reference is 250.32.

You can not tie the "Grounded" conductor to the equipment after the Service Disconnect. You must carry an equipment ground conductor with any feeders and keep the Grounded conductor (Neutral) and the equipment grounding conductor separated. If your generator is a SDS you must use a 3-pole transfer switch (assume single phase) and transfer the neutral.

By the way Welcome to the forum. With a name like George your okay.


George Little

#193653 - 04/12/10 06:38 PM Re: EGC Bond in Transfer Switch (Code) [Re: George Little]  
George393  Offline
New Member
Joined: Apr 2010
Posts: 5
AL
Thanks George!



Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 15 (0.003s) Memory: 0.7518 MB (Peak: 0.8768 MB) Zlib enabled. Server Time: 2017-09-20 11:13:37 UTC