ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
201 volt equipment?
by bigpapa. 04/29/17 12:15 AM
Schneider LC1D09
by jraef. 04/28/17 11:05 PM
Permit Snafus...AHJs and Contractors Jump in
by sparky. 04/28/17 08:11 PM
Electrode boilers question
by annemarie1. 04/27/17 01:40 PM
Why cables look like they do
by LongRunner. 04/26/17 09:36 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,929 Are you busy
169,757 Re: Forum
162,965 Need opinion
Who's Online Now
0 registered members (), 56 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#193490 - 04/05/10 09:15 AM transformer above ceiling?  
cgw  Offline
Member
Joined: Jul 2004
Posts: 133
Rochester NY
30KVA dry type transformer (480 X 120/208)
Can it be located above a suspended accessible ceiling (say in a medical office building)?
Can it be located above this ceiling if the ceiling space is a return air plenum?


2017 / 2014 NEC & Related Books and Study Guides

#193502 - 04/05/10 07:10 PM Re: transformer above ceiling? [Re: cgw]  
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
NEC 2008 450.13(B) says, generally for this size and type, you can. The plenum space question is not addressed.


#193506 - 04/05/10 09:40 PM Re: transformer above ceiling? [Re: Gregtaylor]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,810
Brick, NJ USA
300.22 (c)(2) should be read, and then I suggest you speak to the local AHJ for his/her interp. Under 50 KVA is no issue, BUT...the air handling ceiling needs to be addressed. Also, you may want to have a cut sheet for the exact xfr you intend to install.



John

#193508 - 04/05/10 10:52 PM Re: transformer above ceiling? [Re: HotLine1]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
I think this is probably legal, depending on the transformer but it might be a questionable design choice. If that transformer smokes it will share the joy with the rest of the building pretty fast, at least that HVAC zone anyway.


Greg Fretwell

#193588 - 04/08/10 08:07 PM Re: transformer above ceiling? [Re: gfretwell]  
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
If the Life Safety System ( Fire Alarm ) is up to snuff a duct detector is going to shut things down well enough in time.

Not quite the same set-up...

But I rigged a 45kVA XFRMR, dry-type, above a grid to give isolated power to data loads. Upon the detection of fire, within this space only, a shunt-trip killed total power - with a time delay of seconds so that the data state could be frozen/ preserved. Subsequently the dry fire system would be flooded into the now unpowered space.

So the question of plenum return air really would seem to be a life safety question not to be answered within our Code.


Tesla


Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,429
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.7687 MB (Peak: 0.9081 MB) Zlib enabled. Server Time: 2017-04-29 13:29:23 UTC