#193031 - 03/16/10 02:55 PM Health Care Facility  
ggardiner  Offline
Member
Joined: Oct 2001
Posts: 81
Calgary, Alberta Canada
First off let me say it has been over 15 years since I was involved in anything using conventional electrical components in Canada and maybe 20 years since I was ever asked anything to do with Health Care Facitlies in Canada.
In the US there is cable specified for Health Care (AC-HFC) and for non Heath care MC is used. Now there is a crossover between the two. In Canada I had the impression normally for normal 120 receptalces we would use the hospital grade receptacle and 12/2 BX with insulated ground is this correct or am I in need of a refesher on Canadain Standards?


Tools for Electricians:

#193056 - 03/17/10 02:56 PM Re: Health Care Facility [Re: ggardiner]  
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
It depends.
The use of armoured cable requires approval from the local authority. IE special permission.
Locally that is very easy to get. The bonding conductor is required to be insulated against accidental contact with the armour if you are using armoured cable (BX) or (AC)
Typically that is ISO (isolated) the construction of ISO bx is insulated power conductors and 1 insulated bonding conductor as well as a bare. Regular AC cable is not permitted as the bonding wires are bare and it is not a #12 as is the minimum size for the insulated bonding wire.
Teck cable sized for the minimum #12 bonding wire is acceptable and in combustible buildings we even permit 10-2 loomex as the bonding wire is #12. Clearly the voltage drop and potential rise test have to be passed and the results submitted to the inspection department.
If you are doing a real hospital as opposed to a GP's office you will be using pipe and wire.


#193074 - 03/18/10 12:11 PM Re: Health Care Facility [Re: mikesh]  
ggardiner  Offline
Member
Joined: Oct 2001
Posts: 81
Calgary, Alberta Canada
Thanks



Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.003s) Memory: 0.7515 MB (Peak: 0.8761 MB) Zlib enabled. Server Time: 2017-06-25 12:16:57 UTC