septic grinder pump motor #191491
12/31/09 02:51 AM
12/31/09 02:51 AM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
I am reading art 430 trying to determine if I can upsize my breaker. I have a service call for a septic grinder which keeps tripping the breaker and setting off high limit alarm.
I don't know any of the specs for the motor(not going to scrape feces off nameplate to find out :-)) What I do know is the running current is 12.5 amps and the start up is about 31 amps, it is protected at 20 amps now and want to change 2 pole breaker to a 25 amp.
Thanks,
H20

2017 / 2014 NEC & Related Books and Study Guides
Re: septic grinder pump motor [Re: watersparkfalls] #191495
12/31/09 11:08 AM
12/31/09 11:08 AM
L
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
1st,I has it been determined that the motor/conductors are ok?
Depending on the cycle times,the breaker may just be getting tired.

Then get into the OCPD.

Re: septic grinder pump motor [Re: leland] #191496
12/31/09 12:02 PM
12/31/09 12:02 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Breaker getting tired? frown

How about there maybe being a problem with the pump?

The control panel ought to have a sticker or at least manuals for the pumps, giving you the normal FLA. Otherwise, the size of the contactor can give you an idea of the maximum amount of current the panel can handle. Personally, I'll bet you're exceeding the proper limits.

Grinder pump or not, the first likely cause of troublr is stringy material getting into the pump and wrapping itself around the shaft. If the pump is 3 phase, you can run it backwards and see if that clears the problem.

Next on the list are bad bearings on the pump. When you pump the pit down, you'll likely hear noise once the motor is exposed. Alternatively, you might be able to feel vibrations as the pump runs.

There's no avoiding someone getting down in the pit. If that someone is you, consider getting vaccinated against hepatitis.

Re: septic grinder pump motor [Re: renosteinke] #191497
12/31/09 01:55 PM
12/31/09 01:55 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Is the 'trip' happening on start-up, or running?? Without info or details on pump it's a 'guess' opinion. 230 volt, single phase??

12.5A running w/20A OCP sounds 'right' IF trip is only on start, and contacts, etc. are OK, try the 25 while you're there to observe.



John
Re: septic grinder pump motor [Re: HotLine1] #191520
01/01/10 06:19 AM
01/01/10 06:19 AM
watersparkfalls  Offline OP
Member
Joined: Mar 2005
Posts: 222
Washington...Not DC
Hotline it is 230 volt, tripping is at start up. This motor is fed through a float, so there is no motor control, the control is strictly for high alarm. I will change breaker to 25 amp, just not sure if it's legal, since I don't know what the nameplate is, or if the motor has overload protection(which excludes the exception of next size up).

Reno, I have heard that the hepatitis shot they give you, is for one form of it. And there are several types, so I gotta draw the line and say "No way!" Bearings could be, don't think anything is caught in motor, but will check with septic guy that inspected pump prior to my service call(they are not licensed for electrical).

Leland, conductors should be fine, it is overcurrent tripping not short circuit.

Thanks guys,
this website is very helpful.
H20

Re: septic grinder pump motor [Re: watersparkfalls] #191521
01/01/10 10:50 AM
01/01/10 10:50 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
It's a shame that you're not there together with the plumber; that's the way to do these jobs. Oh well.

You need to pull the pump to check the impeller for foreign crud. The first step is to try to spin it by hand; if it feels harder than is should be, some disassembly will be required to clear the pump. This is not always practical in the field.

You are correct in that there are several types of hepatitis. However, there is only one that is transmitted by contact with sewage; that's the one you get the shot for. Your MD can keep all the types straight. Just day "no, Doc, I'm not a junkie, I work with sewage" and he'll know which vaccine to use.

Re: septic grinder pump motor [Re: renosteinke] #191522
01/01/10 12:03 PM
01/01/10 12:03 PM
L
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Breaker getting tired? frown

Technical? No. But I have seen it on these types of ckts.
Also it was not my 1st choice.

I'll try harder next time blush thumbs

Re: septic grinder pump motor [Re: leland] #191994
01/22/10 03:19 PM
01/22/10 03:19 PM
G
Gregtaylor  Offline
Member
Joined: Mar 2005
Posts: 212
Boise, Idaho, USA
Slightly off subject, but be aware, hepatitis is not airborne transmittable. Cover your skin, wear a mask, take a shower, you'll be OK. Not happy, but OK.

Re: septic grinder pump motor [Re: Gregtaylor] #192033
01/23/10 07:26 PM
01/23/10 07:26 PM
S
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,328
Alaska
If the pump in plugged into a receptacle then the breaker can not execeed the requirement on NEC 240.4(D)


"Live Awesome!" - Kevin Carosa

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
waymag
waymag
dallas, texas, USA
Posts: 67
Joined: January 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,576 Are you busy
180,374 Re: Forum
170,852 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.029s Queries: 15 (0.005s) Memory: 1.0032 MB (Peak: 1.1780 MB) Zlib enabled. Server Time: 2018-01-21 14:30:09 UTC