Just What is the Ampacity of Phone Wire, Anyway? #19134
12/20/02 08:22 PM
12/20/02 08:22 PM
sparky66wv  Offline OP
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

[Linked Image]

Unfortunately, it wasn't related to the problem I was troubleshooting...


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Work Gear for Electricians and the Trades
Re: Just What is the Ampacity of Phone Wire, Anyway? #19135
12/20/02 08:34 PM
12/20/02 08:34 PM
C
CTwireman  Offline
Member
Joined: Feb 2002
Posts: 840
Connecticut, USA
[Linked Image] [Linked Image] [Linked Image]

This was live????


Peter
Re: Just What is the Ampacity of Phone Wire, Anyway? #19136
12/20/02 08:58 PM
12/20/02 08:58 PM
G
ga.sparky56  Offline
Member
Joined: Nov 2002
Posts: 558
young harris georgia usa
sparky66,I thought I had seen it all, until this.Ive seen zip cord but never phone wire.

Re: Just What is the Ampacity of Phone Wire, Anyway? #19137
12/20/02 09:06 PM
12/20/02 09:06 PM
A
arseegee  Offline
Member
Joined: Jan 2002
Posts: 324
Statesboro, GA USA
As you can see from the pictures, CAT3 is good for 20A 125V. You MUST use CAT5 on 30A circuits!

Re: Just What is the Ampacity of Phone Wire, Anyway? #19138
12/20/02 09:11 PM
12/20/02 09:11 PM
S
sparkync  Offline
Member
Joined: Oct 2002
Posts: 830
NC
WOW [Linked Image]

Re: Just What is the Ampacity of Phone Wire, Anyway? #19139
12/20/02 09:24 PM
12/20/02 09:24 PM
N
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
The amazing thing is that the wire doesn't appear to be burned up. I guess that nothing larger than a table lamp was ever plugged in here.

I saw thermostat wire used like this once, but even that is heavier than phone wire. [Linked Image]

Re: Just What is the Ampacity of Phone Wire, Anyway? #19140
12/20/02 10:00 PM
12/20/02 10:00 PM
S
SvenNYC  Offline
Member
Joined: Aug 2002
Posts: 1,691
New York City
Isn't bell/phone wire the same gauge as the wire used for the miniature X-mas tree lights?

Of course those are wired in series so there's probably not that much juice going through them.

Sparky66 - That's a venerable and interesting-looking switch. Neve seen an in-wall switch with front wire terminals before. I'd be leery about using one of those with a metal cover-plate. [Linked Image]

Did you put new wire/devices in there or did you have to close it back and leave as-is?

Re: Just What is the Ampacity of Phone Wire, Anyway? #19141
12/20/02 10:09 PM
12/20/02 10:09 PM
G
GlennH  Offline
Member
Joined: Nov 2001
Posts: 40
pa.
Amazin...

never seen nuthin like it.

Hope you edumacated the homeowner that he should use RED and GREEN as tip & ring!!


Maybe da plug went bad on his phone and he put male plug on and used rec. to plug phone in, switch was to shut the dang thang off at suppertime so as not to be interrupted by danged telemarketers.

Glenn (former ingeesh teacher)

Re: Just What is the Ampacity of Phone Wire, Anyway? #19142
12/20/02 10:53 PM
12/20/02 10:53 PM
sparky66wv  Offline OP
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
<paul harvey>
"...and now, the rest of the story..."
</paul harvey>

This is the same dwelling as the one in these threads:


Link 1

Link 2

This was found, as well as three flying and hidden splices, and other loveliness. Still no fault found. The AFCI trips when load is applied, and taking the circuit apart piece by piece today had narrowed it down to a splice I can't reach without liberal use of a Sawzall.

So... We'll tackle it again tomorrow...

Oh, this receptacle and switch is/was in a bathroom. Yes, a bathroom. The most abused receptacle in a house. My belief is that it must've never been energized, or atleast never loaded. The "feeder" was snipped off in the wall. I tore boxes and all out and threw them in the trash.

All in a days work.

[Linked Image]

<paul harvey>
"...Good day..."
</paul harvey>


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Re: Just What is the Ampacity of Phone Wire, Anyway? #19143
12/20/02 10:55 PM
12/20/02 10:55 PM
sparky66wv  Offline OP
Member
Joined: Nov 2000
Posts: 2,236
West Virginia
Woops... I did the <paul harvey> thing already in the other thread!

[Linked Image]

[This message has been edited by sparky66wv (edited 12-20-2002).]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Page 1 of 3 1 2 3

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,547 Are you busy
180,353 Re: Forum
170,835 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 15 (0.004s) Memory: 1.0256 MB (Peak: 1.2019 MB) Zlib enabled. Server Time: 2018-01-19 11:27:31 UTC