2 Wires in one 66 Block Terminal #191257
12/23/09 05:36 AM
12/23/09 05:36 AM
M
mhulbert  Offline OP
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
I've got a question for somebody who wires more 66 blocks than me. Do you consider it OK to put 2 24 gauge wires in one terminal? I usually punch them separate- punch the 1st wire, then lay in the 2nd and punch it.

I thought that I once read there was a limit to the number of wires you can put in a terminal...any ideas?

Mike

Study Guides for VDV / Structured Cabling Installers

Voice, Data, Video, (VDV) Fiber Optics, Communications, Low Voltage,
Fire Alarm, Electronic Security Systems Installations & Related

NTC Low Voltage Training & NICET Exam Study Guides
Low Voltage Training & NICET Exam Study Guides

Re: 2 Wires in one 66 Block Terminal [Re: mhulbert] #191272
12/23/09 01:50 PM
12/23/09 01:50 PM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
No, it is never OK to place more than one wire in a 66 block terminal. They have a "V" shaped throat, so once the first wire is pushed into it, another wire on top will not be held securely.

The only proper way is to loop a jumper between two rows of clips so that there are more termination points made available.


---Ed---

"But the guy at Home Depot said it would work."
Re: 2 Wires in one 66 Block Terminal [Re: EV607797] #191278
12/23/09 02:27 PM
12/23/09 02:27 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,165
Estero,Fl,usa
Don't forget you have a "no cut" end on your 66 blade. You can just leave one wire long, don't cut it and use it for your jumper to the next row of terminals. You usually skip every other one on telco. I have a whole string of pairs jumpered together on my phone block on the line side, then use the bridging clips to isolate the spurs out to each jack punched on the other side.


Greg Fretwell
Re: 2 Wires in one 66 Block Terminal [Re: mhulbert] #191293
12/23/09 05:48 PM
12/23/09 05:48 PM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Mike,
That's not the way I'd do it.
As far as I'm aware them terminals are only designed for one solid wire.
One the same side of the coin, stranded wires (as used in patch leads) won't work either.

I was part of a building renovation a couple of years ago and the "phone tech" was there working on the Comms panel, I noticed he was pushing the wires into the 110 blocks with a terminal screwdiver, I asked him if he had a proper punch-down tool.
"Yeah, but it's out in the van, I'm in here".

Unreal. mad

Re: 2 Wires in one 66 Block Terminal [Re: Trumpy] #191319
12/24/09 01:47 AM
12/24/09 01:47 AM
M
mhulbert  Offline OP
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
Thank you everyone for the input! I hooked the phone lines into my blocks today, and sure enough, intermittent problems where I doubled up! I am using a "split" block, with my extensions on my left and phone line on the right, using bridge clips to enable a line to each extension. I doubled up on the right side, at the top of each block (There are 5 blocks total, about 25 4 pair extensions, and 4 phone lines going to each block). On Monday I will have to reconfigure these so that we are not doubled up. I will try to get some pictures of this.

Flat blade screwdriver in a 110 block!? Ugh, should be a lot of service calls in his future! Punchdown tools stay in the Phone/Data bag no matter what. You can do almost everything you need with a punch, 10-in-1 screwdriver, and cable scissors.


Re: 2 Wires in one 66 Block Terminal [Re: mhulbert] #191321
12/24/09 02:20 AM
12/24/09 02:20 AM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
Originally Posted by mhulbert
Flat blade screwdriver in a 110 block!? Ugh.


Hey, I've seen IT guys use credit cards for 110 blocks too. The smarter ones cut a notch in them to clear the contact. I'm not kidding!


---Ed---

"But the guy at Home Depot said it would work."
Re: 2 Wires in one 66 Block Terminal [Re: EV607797] #191322
12/24/09 02:45 AM
12/24/09 02:45 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,165
Estero,Fl,usa
I have a little tool that comes with a keystone block that I have used on 110s when I didn't have my Harris. It is basically just a piece of plastic with a slot cut in it. I can see a credit card working for a few punches.


Greg Fretwell
Re: 2 Wires in one 66 Block Terminal [Re: gfretwell] #191323
12/24/09 02:48 AM
12/24/09 02:48 AM
M
mhulbert  Offline OP
Member
Joined: Oct 2004
Posts: 132
Anaheim, CA USA
I will remember the CC trick for guerrilla warfare LAN work. I have a non-impact punchdown tool that I bought in a pinch when nothing else was open...that things kills your hands after a few jacks.

I've been going 100% Fluke JackRapid though, what a labor saver. I use keystone patch panels so that I can use it on both ends. No sore hands/wrists after a day with that, and no jamming a 110 cutting edge through your palm


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 19
Potseal 13
Popular Topics(Views)
243,511 Are you busy
180,298 Re: Forum
170,800 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.003s) Memory: 0.9982 MB (Peak: 1.1612 MB) Zlib enabled. Server Time: 2018-01-16 16:57:37 UTC