ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 8
Recent Posts
OD of Alum and Copper
by HotLine1. 08/23/17 07:30 PM
Grid problem??
by annemarie1. 08/21/17 01:10 PM
Bathroom electrical
by doc. 08/19/17 06:53 AM
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,167 Are you busy
175,834 Re: Forum
167,969 Need opinion
Who's Online Now
0 registered members (), 47 guests, and 6 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#190353 - 11/12/09 05:16 PM 200amp disconect  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 216
Washington...Not DC
I have a 400Amp service with 2 200Amp disconects. Can I put doouble barel lugs on 1 disconect to feed 1 200Amp panel and feed 100Amp back fed breaker.
Thanks H2O


2017 / 2014 NEC & Related Books and Study Guides

#190354 - 11/12/09 05:47 PM Re: 200amp disconect [Re: watersparkfalls]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
My answer would be yes assuming your load is appropriate. Assuming also you are not overloading the 200a. overcurrent device and the 100a breaker is secured in the panel by a Listed clip.


George Little

#190355 - 11/12/09 07:12 PM Re: 200amp disconect [Re: George Little]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
The only joker in the deck is that the wire to the 100 amp panel should be sized for 200 amps, unless you can apply tap rules to your circumstance. Otherwise, there might be a problem fitting the wire into the breaker.


#190357 - 11/12/09 08:16 PM Re: 200amp disconect [Re: renosteinke]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Reno- If I'm reading his post correctly, this would be a tap to a 200a Service switch. Since he is on the load side of fusing, we are talking feeder. In his case there are no actual feeder conductor, only double barrel lugs. This happens sometimes. Since he is terminating in a 100a overcurrent device he could use 100a. wire. The code reference could be 240.21(B)(1). There is no way he could overload the 100a. conductors since there protected due to the tap limitation mentioned above.

Last edited by George Little; 11/12/09 08:17 PM. Reason: Big fingers

George Little

#190367 - 11/13/09 03:12 AM Re: 200amp disconect [Re: George Little]  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 216
Washington...Not DC
thanks guys.
H2o


#190368 - 11/13/09 03:38 AM Re: 200amp disconect [Re: watersparkfalls]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,105
Estero,Fl,usa
I think Reno may be referring to the raceway requirements and 25' length restrictions for taps. The ampacity part is OK if this is a legal tap.


Greg Fretwell

#190369 - 11/13/09 12:14 PM Re: 200amp disconect [Re: gfretwell]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Thank you, Greg.



Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.7846 MB (Peak: 0.9424 MB) Zlib enabled. Server Time: 2017-08-24 10:38:55 UTC