#189136 - 09/21/09 03:40 PM Removal of panelboard classifications  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,124
Estero,Fl,usa
I see there is no more "lighting and appliance" panelboard in the 2008 so I suppose the defacto 2 breaker disconnect limit is gone too.
Is this saying you can put a 6 breaker panel in the detached garage without any other means of disconnect? (assuming it is adequately protected at the house)


Greg Fretwell

2017 / 2014 NEC & Related Books and Study Guides

#189137 - 09/21/09 04:49 PM Re: Removal of panelboard classifications [Re: gfretwell]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I'm not sure I know what '2 breaker' limit you're referring to. Nor do I see how the '6 disconnect' rule aplies.

The 'six throws of the hand' rule applies to services, not to 'sub' panels. You have that panel protected by just one disconnecting /OCPD means, though that can be at either end of the feeder, or any place inbetween.

What that little change in vocabulary means is that the 42 breaker limitation is gone, as are all the arguments over whether something is a 'poer' or 'lighting' panel. That panel can have a gazillion breakers in it, and it doesn't matter how many of the circuits need neutrals.


#189141 - 09/21/09 05:57 PM Re: Removal of panelboard classifications [Re: renosteinke]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,124
Estero,Fl,usa
There used to be a rule that said a lighting and appliance panelboard had to be protected by 1 or 2 main breakers. AHJs read that to mean if you had a sub panel in a detached building with 6 breakers you needed a main breaker so the 6 disconnect rule was moot.


Greg Fretwell


Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.004s) Memory: 0.7527 MB (Peak: 0.8776 MB) Zlib enabled. Server Time: 2017-10-23 09:45:26 UTC