#188420 - 08/07/09 07:58 PM Sign Disconnect  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Article 600.6 ask for a disconnect for a sign. If a sign builder installs a switch as an integral part of the sigh does this satisfy the requirement? One must realize that the UL standard does not require a disconnect as part of the requirements for sign construction.


George Little

2017 / 2014 NEC & Related Books and Study Guides

#188422 - 08/07/09 09:25 PM Re: Sign Disconnect [Re: George Little]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
If it was at the circuit entry into the sign, disconnected all ungrounded conductors and was marked as the disconnect with an "off" position I would allow it.


Greg Fretwell

#188451 - 08/09/09 07:29 PM Re: Sign Disconnect [Re: gfretwell]  
luckyshadow  Offline
Member
Joined: Jan 2005
Posts: 305
Maryland USA
yes a factory installed disconnecting switch that disconnects all ungrounded conductors is allowed


#188489 - 08/11/09 04:57 PM Re: Sign Disconnect [Re: luckyshadow]  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
I guess I left out a very key point. The branch circuit enters the back of the sign enclosure, travels through the sign and then exits the sign to terminate on the line side of a WP switch mounted on the sign. The load side of the switch has conductors that re-enter the sign enclosure and connect up to the Xformer of the sign. I feel that this a violation of 600.6 since the switch does not disconnect all un-grounded conductors in the sign. What do you think?


George Little

#188494 - 08/11/09 07:36 PM Re: Sign Disconnect [Re: George Little]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
Note I said "at the circuit entry into the sign". I agree with you, either move the disconnect to the conduit entry point or change where the conduit enters to make it next to the switch, preferably in a separate enclosure within the sign.
This could be as simple as a 4x4 deep ring that covered the switch terminals and conduit entry with a blank cover on the other side.
I believe the purpose of the disconnect is to make the interior of the equipment safe. I am not making a proposal but I do think a label over the disconnect enclosure saying something like "line voltage present with disconnect off" is a good idea.


Greg Fretwell


Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.002s) Memory: 0.7688 MB (Peak: 0.9086 MB) Zlib enabled. Server Time: 2017-04-28 18:02:49 UTC