#188200 - 07/24/09 09:57 PM 90-2(A)-1-14 Log #225 NEC-P01 Final Action: Reject  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Please send in a comment to ACCEPT this proposal, thank you.
_______________________________________________________________
1-14 Log #225 NEC-P01 Final Action: Reject
(90.2(A))
_______________________________________________________________
Submitter: Joseph A. Tedesco, Boston, MA
Recommendation: Revise as follows:
90.2 Scope (A) Covered. This code covers the installation and use of
electrical...no change.
Substantiation: See 110.3(B) Installation and Use.
Panel Meeting Action: Reject
Panel Statement: The submitter’s substantiation does not account for the fact
that 110.3(B) refers only to listed equipment.
See the NFPA Regulations Governing Committee Projects Section 4.3.3 that
states that proposals must include a statement of the problem and substantiation
for the proposal.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 10 Negative: 2
Explanation of Negative:
HICKMAN, P.: We conclude that the submitter’s reference to 110.3(B) was
offered as an example of where “and use” is used to substantiate the
recommendation and agree with the submitter that the scope of the document
should include “and use” since the NEC does cover use as well as installation.
MCMAHILL, L.: This proposal should have been accepted. Although the
submitter did not provide clear substantiation for the proposed change, it is
apparent that parallel structure from one code section to another is the intent.
By accepting the change, parallel structure would have been attained.

Last edited by Joe Tedesco; 07/24/09 09:57 PM.

Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#188227 - 07/26/09 09:36 AM Re: 90-2(A)-1-14 Log #225 NEC-P01 Final Action: Reject [Re: Joe Tedesco]  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Originally Posted by Joe Tedesco
Please send in a comment to ACCEPT this proposal, thank you.
_______________________________________________________________
1-14 Log #225 NEC-P01 Final Action: Reject
(90.2(A))
_______________________________________________________________
Submitter: Joseph A. Tedesco, Boston, MA
Recommendation: Revise as follows:
90.2 Scope (A) Covered. This code covers the installation and use of
electrical...no change.
Substantiation: See 110.3(B) Installation and Use.
Panel Meeting Action: Reject
Panel Statement: The submitter’s substantiation does not account for the fact
that 110.3(B) refers only to listed equipment.
See the NFPA Regulations Governing Committee Projects Section 4.3.3 that
states that proposals must include a statement of the problem and substantiation
for the proposal.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 10 Negative: 2
Explanation of Negative:
HICKMAN, P.: We conclude that the submitter’s reference to 110.3(B) was
offered as an example of where “and use” is used to substantiate the
recommendation and agree with the submitter that the scope of the document
should include “and use” since the NEC does cover use as well as installation.
MCMAHILL, L.: This proposal should have been accepted. Although the
submitter did not provide clear substantiation for the proposed change, it is
apparent that parallel structure from one code section to another is the intent.
By accepting the change, parallel structure would have been attained.


This is an exact copy that I sent in to NFPA and it already has many supporters, including IBEW and IAEI. Please let the members of this forum decide. You make some good points though. I believe that it will be accepted.


FORM FOR COMMENT FOR 2011 NATIONAL ELECTRICAL CODE®
INSTRUCTIONS — PLEASE READ CAREFULLY

Type or print legibly in black ink. Use a separate copy for each comment Limit
each comment to a SINGLE section. All comments must be received by NFPA by
5 p.m., EDST, Friday, October 23, 2009, to be considered for the 2011 National
Electrical Code. Comments received after 5:00 p.m., EDST, Friday, October 23, 2009,
will be returned to the submitter. If supplementary material (photographs, diagrams, reports, etc.) is
included, you may be required to submit sufficient copies for all members and alternates of the
technical committee.
For technical assistance, please call NFPA at 1-800-344-3555.
FOR OFFICE USE ONLY
Log #:
Date Rec’d:
Please indicate in which format you wish to receive your ROP/ROC electronic paper download
(Note: If choosing the download option, you must view the ROP/ROC from our website; no copy will be sent to you.)
Date Name Tel. No.
Company Email
Street Address City State Zip
***If you wish to receive a hard copy, a street address MUST be provided. Deliveries cannot be made to PO boxes.
Please indicate organization represented (if any)
1. Section/Paragraph
2. Comment on Proposal No. (from ROP):
3. Comment recommends (check one): new text revised text deleted text
4. Comment (include proposed new or revised wording, or identification of wording to be deleted): [Note: Proposed text should be in
legislative format; i.e., use underscore to denote wording to be inserted (inserted wording) and strike-through to denote wording to be deleted
(deleted wording).]

Accept the proposal so the 2011 NEC will read as follows:
"90.2(A) Covered. This Code covers the installation and use of electrical conductors, equipment, and raceways; signaling and
communications conductors, equipment, and raceways; and optical fiber cables and raceways for the following:" no further changes

5. Statement of Problem and Substantiation for Comment: (Note: State the problem that would be resolved by your recommendation; give the specific
reason for your Comment, including copies of tests, research papers, fire experience, etc. If more than 200 words, it may be abstracted for publication.)

In addition to 110.3(B), see the 2009 UL White book, Marking Guides, and correlation between these documents via the internet.

http://www.ul.com/global/eng/pages/o...regulator/ccd/

http://www.ul.com/global/eng/pages/o...or/electrical/

6. Copyright Assignment

(a) I am the author of the text or other material (such as illustrations, graphs) proposed in the Comment.

(b) Some or all of the text or other material proposed in this Comment was not authored by me. Its source is as follows:

(please identify which material and provide complete information on its source)
I hereby grant and assign to the NFPA all and full rights in copyright in this Comment and understand that I acquire no rights in any publication of NFPA
in which this Comment in this or another similar or analogous form is used. Except to the extent that I do not have authority to make an assignment in
materials that I have identified in (b) above, I hereby warrant that I am the author of this Comment and that I have full power and authority to enter into
this assignment.

Signature (Required) __________________________________________

PLEASE USE SEPARATE FORM FOR EACH COMMENT

Mail to: Secretary, Standards Council · National Fire Protection Association
1 Batterymarch Park · Quincy, MA 02169-7471 OR
Fax to: (617) 770-3500 OR Email to: proposals_comments@nfpa.org


Joe Tedesco, NEC Consultant


Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.007s) Memory: 0.7503 MB (Peak: 0.8691 MB) Zlib enabled. Server Time: 2017-11-18 19:15:01 UTC