Which Cartridge Fuse? #187496
06/28/09 10:29 PM
06/28/09 10:29 PM
T
thiggy  Offline OP
Member
Joined: May 2004
Posts: 24
B'ham Al
I have an old family farm house with a 125 amp Square D breaker box. The service disconnect is a 100 amp Square D cartridge fuse. I have never had the main blow, but I decided that I better have a spare pair of fuses on hand just in case, as in this rural area it would be difficult to locate one in a hurry. I drove to the nearest city and located fuses at Lowes, but I am not sure which one of the two types they had should be used for my application. The heavy-duty time-delay one said it is "for motor and main panel protection. (FRN-R)" It indicated that "for lighting or electric heating circuits use general purpose fuses.(NON)" I use window AC units for cooling, and 1500 watt portable heaters for infrequent use in winter heating. Water heaters are also electric. (This is generally just a week-end house.) Which type of fuse would be the most appropriate for my use?

Work Gear for Electricians and the Trades
Re: Which Cartridge Fuse? [Re: thiggy] #187497
06/29/09 12:41 AM
06/29/09 12:41 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
I would go with the FRN.
That will tolerate a short time spike in current.
The biggest opportunity for a spike in current is when you have a power glitch and the service would see locked rotor from every motor that was running at that time.


Greg Fretwell
Re: Which Cartridge Fuse? [Re: gfretwell] #187499
06/29/09 03:28 AM
06/29/09 03:28 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Yeah,
I agree with Greg.
You really need something with a bit of time delay on it for a main fuse.
After all, the fuse/CB that is electrically closest to the fault (ie, a sub-circuit fuse/CB) should operate first, in any electrical system.
Anything less is poor design.

Re: Which Cartridge Fuse? [Re: Trumpy] #187503
06/29/09 11:19 AM
06/29/09 11:19 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,263
Fullerton, CA USA
You answered your own question.

Quote
The heavy-duty time-delay one said it is "for motor and main panel protection. (FRN-R)"

Re: Which Cartridge Fuse? [Re: Trumpy] #187509
06/29/09 12:09 PM
06/29/09 12:09 PM
T
thiggy  Offline OP
Member
Joined: May 2004
Posts: 24
B'ham Al
Thanks for the responses. I shall go with the time delay fuse. (I actually bought two of both types with the intention of returning one pair after I determined which type I should use.)

Re: Which Cartridge Fuse? [Re: thiggy] #187517
06/29/09 07:24 PM
06/29/09 07:24 PM
J
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
There is almost no reason to ever install an NON fuse. For all intents NONs are old technology, and are almost always sold based on price only.

Re: Which Cartridge Fuse? [Re: JBD] #187526
06/29/09 10:36 PM
06/29/09 10:36 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
We used NONs to protect electronics and there was even a faster blowing fuse that we used for the input to switcher power supplies way back when they were a big cabinet full very expensive parts.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,263
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,516 Are you busy
180,314 Re: Forum
170,811 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 15 (0.003s) Memory: 0.9844 MB (Peak: 1.1396 MB) Zlib enabled. Server Time: 2018-01-17 13:12:41 UTC