Self grounding receptacles. #1874
06/04/01 08:04 PM
06/04/01 08:04 PM
R
Redsy  Offline OP
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
An older home with metal boxes that don't have threaded grounding holes has both top & bottom cable clamps utilized. The grounds are twisted together, cut very short and are not connected to the box. I may be able to use crimp sleeves to install a ground pigtail. If I connect the pigtail to a self-grounding receptacle, will the grounded receptacle effectively ground the box, or does the concept of self-grounding receptacles only work the reverse way
(grounded boxes don't require pigtail)?

Work Gear for Electricians and the Trades
Re: Self grounding receptacles. #1875
06/04/01 08:29 PM
06/04/01 08:29 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,342
Redsy;
so your Q would be does the recp carry a ground to the box, as it would normally carry a ground from box to rec.

either way it goes thru the 6-32's , this may be pertinent to how it's worded...

i wish they were truley self grounding for those K&T jobs, but i guess that would be like wishin' for a self cleaning chicken
[Linked Image]

Re: Self grounding receptacles. #1876
06/05/01 07:00 AM
06/05/01 07:00 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
In an application where there's no threaded hole for the ground screw or it's impractical to use the hole, I use ground clips.(Don't particularly like them, tho) I don't have the book here, but I think the ground to the box can't be dependent on the device. (said w/ my Crawfish net in hand and ready for action)

Re: Self grounding receptacles. #1877
06/05/01 07:25 AM
06/05/01 07:25 AM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,890
NY, USA
Redsy,

That is a good question!

Would the self-grounding receptacle itself qualify as a "listed grounding device" as in 250-148(a)? I'm thinking that it would not because that is not it's sole purpose.

I think that Electures' grounding clips would be the best way out. (I don't like them either)

Bill

Re: Self grounding receptacles. #1878
06/06/01 07:23 PM
06/06/01 07:23 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,342
i think you guys nailed it with 250-148 & the clips, good job!

[Linked Image]


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,231
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,543 Are you busy
180,346 Re: Forum
170,832 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 14 (0.004s) Memory: 0.9665 MB (Peak: 1.1066 MB) Zlib enabled. Server Time: 2018-01-19 03:52:37 UTC