ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
VFD MotorFeeders
by gfretwell. 10/19/17 01:02 AM
Generator Cable Sizing
by brsele. 10/18/17 07:39 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,417 Are you busy
177,389 Re: Forum
168,990 Need opinion
Who's Online Now
0 registered members (), 25 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#187363 - 06/24/09 01:55 PM transformer help needed  
jkmscottie  Offline
New Member
Joined: Jun 2009
Posts: 2
ks
I am trying to get from 208v with 2 wires to 240 on 1 wire to ground any ideas on how to achieve this?


Work Gear for Electricians and the Trades

#187364 - 06/24/09 02:36 PM Re: transformer help needed [Re: jkmscottie]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa


Greg Fretwell

#187365 - 06/24/09 03:29 PM Re: transformer help needed [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
I just looked it up and they have 208 to 120/240 from 1 KVA to 75 KVA.
Search by keyword "208 primary" and look at the single phase units.
You don't say anything in your profile but I am assuming you know the ramifications of installing a transformer.


Greg Fretwell

#187366 - 06/24/09 05:31 PM Re: transformer help needed [Re: gfretwell]  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,872
Brick, NJ USA
Are you sure you want "240 on 1 wire to ground"

240 is 2 'hots', 240 volt leg to leg, and 120 volt leg to ground and/or neutral.

Your profile says that you are an electrician, is that correct??



John

#187368 - 06/24/09 07:32 PM Re: transformer help needed [Re: HotLine1]  
GA76JW  Offline
Member
Joined: Mar 2004
Posts: 193
Suwanee, GA USA
I'd be interested to hear what application you are using this for?????

I can't say as I have heard of anything that uses 240 on one leg yet.


"If common sense was common, everyone would have it"-not sure, someone here


#187369 - 06/24/09 07:40 PM Re: transformer help needed [Re: GA76JW]  
jkmscottie  Offline
New Member
Joined: Jun 2009
Posts: 2
ks
Yes i am an electricain. I am working on a heater project for the company i am working for now. It is for leakage current testing on heaters. They specified and asked if i can get. I am told that an isolation transformer will do the job. Staco said they can do it. Just checking with you all to see what your opinions are on this.
Thank You


#187373 - 06/24/09 10:05 PM Re: transformer help needed [Re: jkmscottie]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
The transformers you get with a "208 primary" search (second pane down) are right up your alley. For test equipment you could even switch the output topology to test with 3 different grounding references.


Greg Fretwell

#187374 - 06/24/09 10:24 PM Re: transformer help needed [Re: gfretwell]  
twh  Offline
Member
Joined: Mar 2004
Posts: 919
Regina, Sask.
Why not a megger?


#187376 - 06/24/09 10:29 PM Re: transformer help needed [Re: twh]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
WAG? Testing under normal load conditions?

BTW, you can get this at Grainger but you will save about 40% if you have your supply house order you one.

BTDT

Better feed the little guy anyway.


Greg Fretwell

#187476 - 06/27/09 10:30 PM Re: transformer help needed [Re: gfretwell]  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
jkmscottie

Welcome to ECN.

Obtain a "Standard", off-the-shelf Single Phase Isolated Transformer, which has a 208V Primary, and 240V Secondary.

Feed the Transformer with a normal 208V 1 Phase 2 Wire + EGC (Equipment Grounding Conductor) Circuit.

On the Secondary side, ground either one of the "X" Terminal outputs... for example, Ground "X2".

Now you have a 240V 2 Wire system with an Ungrounded Conductor and a Grounded Conductor.

The correct way to describe your desired 240V Circuit is:

240V 1 Phase 2 Wire Grounded Circuit.

One "Side" of the Circuit is Ungrounded ("Hot" to Ground),
The other "Side" of the Circuit is Grounded - just like the "Neutral" on a 1 Phase 3 Wire Circuit, or the Common "Neutral" on a 208Y/120V 3 Phase 4 Wire Circuit.

Match the KVA rating to the KVA requirement for the test loads. Since the test loads are Resistance type loads, the power ratings will (almost always) be in KW (Kilo Watts).
If the Heaters consist of only Heater Elements, then the KW ratings will equal KVA.

If these loads only have Ampere ratings, multiply the Amperes by 240, which will show the KW / KVA rating.
example:
Heater Element listed for 240V, FLA = 10
240 x 10 = 2400 VA (Volt-Amps)
Minimum KVA requirement: 2.4 KVA
Transformer size: 3.0 KVA

Good luck.

Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!


Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.022s Queries: 15 (0.004s) Memory: 0.8117 MB (Peak: 0.9925 MB) Zlib enabled. Server Time: 2017-10-21 02:59:03 UTC