#187283 - 06/19/09 10:27 AM 3/8" Ground Rod  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I am currently running electrical service to a new space in a mobile home park. This place has, supposedly, never had a mobile home in it before.

My first hint that this might moy be s completely 'new' space came when a large tree was removed from next to the power pole. Voila! - an old mast / weatherhead was found arrached to the power company's pole.

Yesterday, while trenching to the new trailer, I (naturally) ran dead-center into a buried ground rod. This ground rod - and I do mean a proper ground rod of copper jacketed steel with an acorn clamp - is only 3/8" diameter. I have no idea as to the length. I'm not sure if there is a stub of wire still attached; if there is, I doubt it's larger than #12.

My questions are: when were such rods allowed? How large a service? Why were they discontinued?


Work Gear for Electricians and the Trades

#187285 - 06/19/09 12:51 PM Re: 3/8" Ground Rod [Re: renosteinke]  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
The rod might not have been used as an electrode for the service entrance. It might be a telephone company rod, I've run across them here in the Mountain State & they're usually about 4' long.


Few things are harder to put up with than the annoyance of a good example.

#187287 - 06/19/09 01:02 PM Re: 3/8" Ground Rod [Re: Tom]  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,878
NY, USA
Originally Posted by Tom
The rod might not have been used as an electrode for the service entrance. It might be a telephone company rod, I've run across them here in the Mountain State & they're usually about 4' long.
Yup,

I had one at my house connected to the Telephone Co. connection point outside.

Bill


#187289 - 06/19/09 02:40 PM Re: 3/8" Ground Rod [Re: Bill Addiss]  
LarryC  Offline
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
Perhaps there used to be the old pay telephone booths there. That would explain both the service weatherhead and the ground rod.

Larry C


#187290 - 06/19/09 03:04 PM Re: 3/8" Ground Rod [Re: LarryC]  
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
Standard procedure for telco grounding is a 3/8" x 5' rod if no other electrode is present. These were very common in mobile home or RV parks. Technically, they are supposed to bond it to the trailer's frame with a #6, and then run a separate conductor from the rod to the station protector. Of course, they don't really do inside wiring anymore. Today, they just bond the protector to any electrode they can find and don't mess with bonding the trailer frame.


---Ed---

"But the guy at Home Depot said it would work."

#187295 - 06/19/09 08:17 PM Re: 3/8" Ground Rod [Re: EV607797]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
Vote me with the others. That sounds like a telco/cable rod. My wife had several that were left behind by the telco guys. I may still have one around here somewhere. My FIL was using a couple for tomato stakes.


Greg Fretwell

#187299 - 06/20/09 01:01 AM Re: 3/8" Ground Rod [Re: gfretwell]  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
I have see them few of them as well they are pretty short in length useally 5 footer size. both telephone and Catv company use that for many years. but it no longer done that way so they will just tied to the main EGC rods or EGC conductor.

Merci,Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)



Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 15 (0.003s) Memory: 0.7867 MB (Peak: 0.9416 MB) Zlib enabled. Server Time: 2017-05-28 12:13:37 UTC