Kerosene area Classifaction???? #186979
06/09/09 09:37 AM
06/09/09 09:37 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
Class??? in Article 500??

2017 / 2014 NEC & Related Books and Study Guides
Re: Kerosene area Classifaction???? [Re: Yoopersup] #186980
06/09/09 10:06 AM
06/09/09 10:06 AM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Kerosene is not generally considered to create a classified location.

Re: Kerosene area Classifaction???? [Re: renosteinke] #186981
06/09/09 10:15 AM
06/09/09 10:15 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
Whats its Flash Point???

Last edited by Yoopersup; 06/09/09 10:16 AM.
Re: Kerosene area Classifaction???? [Re: Yoopersup] #186982
06/09/09 10:48 AM
06/09/09 10:48 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
Looked in 2005 NEC Handbook Page 658 (KEROSENE) is there.Flash Point 72% C. looks like Class 2 (A)or Class 1 Division Group D. ?? listed two places. Check it our .
Theres an Area with Diesel Fuel, & Kerosene.
Diesel Fuel I think NO.
Kerosene looks like yes .
Any comments ????

Re: Kerosene area Classifaction???? [Re: Yoopersup] #186986
06/09/09 08:43 PM
06/09/09 08:43 PM
W
walrus  Offline
Member
Joined: Jul 2002
Posts: 680
Bangor Me. USA
K-1 maybe, kerosene is a generic term, it would depend on the product. The oil company should be able to tell you flash point

Re: Kerosene area Classifaction???? [Re: Yoopersup] #186987
06/09/09 08:52 PM
06/09/09 08:52 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Ernie:
Based on a quick read, I'm leaning to "same as diesel". If I had to make an official 'call'; I would do some additional research.




John
Re: Kerosene area Classifaction???? [Re: HotLine1] #186997
06/09/09 10:07 PM
06/09/09 10:07 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Careful here ... home oil heating units do not require any "haz loc" wiring - and kerosene / fuel oil / diesel / jet fuel are all essentially the same thing. Nor should we forget the sundry decorative oil-filled 'candles' that are actually filled with scented kerosene.

Last edited by renosteinke; 06/09/09 11:40 PM.
Re: Kerosene area Classifaction???? [Re: renosteinke] #187003
06/10/09 07:02 AM
06/10/09 07:02 AM
Trumpy  Offline

Member
Joined: Jul 2002
Posts: 8,231
SI,New Zealand
Yoopersup,
What sort of an installation is this referring to?

I know for a fact that choppers I have flown run on a variant of Kerosene and it has a flash point of about 250C.

One other thing I do know, through experience as a FF, is that kerosene has the habit to change from a liquid to vapour very easily, about the same as propane, but not with the explosive force.

Unlike propane, the fumes from kerosene will drift upwards.


Re: Kerosene area Classifaction???? [Re: Yoopersup] #187009
06/10/09 10:37 AM
06/10/09 10:37 AM
Y
Yoopersup  Offline OP
Member
Joined: Mar 2003
Posts: 840
Michigan
Looked it up on the net . Flash point 37-65c .
Auto Ignition Temperature 220C

Still Page 658 NEC Code Handbook info????
Class 1 division group D
Flash point 72
Class zone group IIA

Location is Storage Deisel & Kerosene.

Last edited by Yoopersup; 06/10/09 10:39 AM.
Re: Kerosene area Classifaction???? [Re: Yoopersup] #187026
06/10/09 10:49 PM
06/10/09 10:49 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,918
Brick, NJ USA
Yoop:
Yes, I read the Handbook info & agree with you on that. There's a lot of info that has to be read regarding that table, which I have not read due to time constraints. I have not had a job with kero dispensers, so I have no 'field' quick answer for ya.

Perhaps reach out a PM to 'Walrus'...he's a service station guy.



John
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,481
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,586 Are you busy
180,381 Re: Forum
170,859 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 16 (0.003s) Memory: 1.0235 MB (Peak: 1.2064 MB) Zlib enabled. Server Time: 2018-01-22 00:32:32 UTC