#186247 - 04/28/09 01:37 PM SRML Wire  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
We used to SRML wire, which I understand is "Silicon Rubber Motor Lead" but I'm not sure about that. The environment was an ice cream freezer in a dairy where the temperature was -40 F. The problem was THHN wiring would get brittle and the insulation would just snap right off when you tried to bend the wires. My question is twofold. Is there any other wire that we could use for this temperature environment and what is the temperature rating for SRML wire?


George Little

2017 / 2014 NEC & Related Books and Study Guides

#186250 - 04/28/09 03:18 PM Re: SRML Wire [Re: George Little]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
It seems suitable from the temperature standpoint
-60c to 180c (some brands are even more wide ranging)

http://www.alibaba.com/product-gs/210084293/JG_Silicone_Rubber_Insulation_Motor_Lead.html

The open question is if it is only listed as fixture wire or is it an chapter 3 conductor.


Greg Fretwell

#186256 - 04/28/09 10:34 PM Re: SRML Wire [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
I looked at this a little more. I would probably be OK with the idea of these conductors in pipe but you have to watch the terminations. This is nickle or nickle plated wire so the splicing devices and terminals have to be OK with that.


Greg Fretwell


Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 216
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.009s Queries: 15 (0.002s) Memory: 0.7508 MB (Peak: 0.8767 MB) Zlib enabled. Server Time: 2017-04-24 15:19:03 UTC