ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 3
dsk 3
Recent Posts
Feed to spa panel
by HotLine1. 06/25/17 05:28 PM
Weatherhead, POA, height?
by HotLine1. 06/24/17 02:37 PM
Windows 7 update problem
by ampherder. 06/21/17 07:01 AM
Norwegian power?
by dsk. 06/19/17 03:40 PM
Anyone ever take a Furnas A14D drum sw apart?
by gfretwell. 06/17/17 08:14 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
238,225 Are you busy
173,442 Re: Forum
166,251 Need opinion
Who's Online Now
0 registered members (), 46 guests, and 11 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#185757 - 03/26/09 10:29 AM Basic power quality methodology  
Jerry5565  Offline
New Member
Joined: Mar 2009
Posts: 4
MA
Basic power quality methodology

The more advanced that electronic equipment becomes, the more dependent it is on clean power. I ran into a good reference source on troubleshooting power quality problems. It explains basic procedures such as creating a current one-line, doing a walk around, and keeping an incident log. It's worth checking out ...

Basic power quality methodology


Work Gear for Electricians and the Trades

#185765 - 03/26/09 02:17 PM Re: Basic power quality methodology [Re: Jerry5565]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,207
Chesapeake, VA
Jerry, thanks, this is a great reminder that all those codes everyone ignores, like NFPA 70B, 110, 111, etc... If you actually DO all that recommended and required maintenance and record keeping, you saving money in the long run!

Grounding is incredible important, as well. Traditional NEC grounding methods are fine for safety, but just plain suck at grounding modern electronic equipment. Long pieces of copper wire back to a ground rod might as well be an open circuit to the EMI in a modern datacenter. Supplemental ground systems, equipotential planes, and other methods are required to shunt the noise to ground. It's counterintuitive, but grounding equipment to the metal grid of a raised deck floor is actually far more effective than a wire straight down to a ground rod, because at those frequencies, the capacitance between the raised deck and the earth is a lower impedance than the inductor a straight piece of cable turns into.


#185789 - 03/27/09 12:19 PM Re: Basic power quality methodology [Re: SteveFehr]  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Connection to dirt is not important in noise control. It is the bonding of all surfaces into an equi-potential plane that is important. IMHO we should stop using the word 'grounding' when we mean is 'bonding'.



Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.003s) Memory: 0.7519 MB (Peak: 0.8776 MB) Zlib enabled. Server Time: 2017-06-26 08:44:23 UTC