Service size for Chiropractic Office: X-Ray #185338
03/11/09 02:00 PM
03/11/09 02:00 PM
W
Wardey  Offline OP
New Member
Joined: Dec 2004
Posts: 1
Palm Harbor, FL
Trying to size a service for a chiropactors office and not sure on the demand for an X-Ray machine. The X-Ray Tech say's he needs an 100 Amp 220V circuit. Here's what I have existing:
100 Amp 3 Phase Service w/ 1 Alum Conductors

So do I figure the X-Ray machine at 100% demand?

And my load calcs would be:
12 receptacles @ 180VA = 2160
640sq.ft. @ 3 VA = 1920
Heat @ 10,000 VA
Sign Ckt. @ 1200 VA
X-Ray Machine @ 24,000VA
Total 39,280 VA

39,280VA / 240V = 163.66 Amps / 1.73 = 94.60 Amps

Correct? The 100 Amp service should be suffecient?

Thanks !!!

Work Gear for Electricians and the Trades
Re: Service size for Chiropractic Office: X-Ray [Re: Wardey] #185339
03/11/09 04:18 PM
03/11/09 04:18 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 840
Michigan
if your using 240 x 1.73 it must be a high leg delta??
IF ITS A 120/208 Y (most common) it be 208 x 1.73 =359.84
Just checking.

Re: Service size for Chiropractic Office: X-Ray [Re: Yoopersup] #185341
03/11/09 05:15 PM
03/11/09 05:15 PM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,264
Fullerton, CA USA
Yoop,
Wrong answer.

If 208 volts you DIVIDE it by 1.73
Not MULTIPLY it.

39,280VA / 208V / 1.73 = 109.15 Amps




Re: Service size for Chiropractic Office: X-Ray [Re: electure] #185343
03/11/09 05:26 PM
03/11/09 05:26 PM
Y
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 840
Michigan
39280 divide by 359.84 =109.15962
Sure looked like devideding to me?????

1.73 x 208= 359.84
39280 Divided by 359.84

Last edited by Yoopersup; 03/11/09 05:31 PM.

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,560 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.012s Queries: 15 (0.002s) Memory: 0.9582 MB (Peak: 1.0897 MB) Zlib enabled. Server Time: 2018-01-20 05:20:35 UTC