#18417 - 12/09/02 11:41 PM Transfer switch feeder  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 826
NC
I think I'm missing something..must be because I'm tired tonight... If I have a 8000 wt. generator and using 120 volts circuits it can handle 66.6 amps, and on 240 volts it can handle 33.3 amps, should not the feeder and main breaker be rated at 66.6 amps..at the maximum capacity?? I think I might be missing something here.. awfully tired [Linked Image] I feel like this is probably a dumb question, but just can't get my head to work right, right now [Linked Image] Is the sizing different on generators?? Thanks....Steve


Work Gear for Electricians and the Trades

#18418 - 12/10/02 02:21 AM Re: Transfer switch feeder  
Trumpy  Offline


Member
Joined: Jul 2002
Posts: 8,217
SI,New Zealand
Steve,
Sit down with a coffee, do your calc's again,
I am sure that you have missed something.
Have you figured Power Factor(Cos Phi), in to your calcs?.
How about losses?. [Linked Image]


Let's face it, these days if you're not young, you're old - Red Green grin

#18419 - 12/10/02 09:33 AM Re: Transfer switch feeder  
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
Think double pole. 33.3 x 2 =66.6


#18420 - 12/10/02 05:00 PM Re: Transfer switch feeder  
pauluk  Offline
Member
Joined: Aug 2001
Posts: 7,520
Norfolk, England
Assuming that the generator's 120V output is split across each half of the 240V winding, then loading 4000 watts on each leg (ignoring power factor concerns) would result in 33.3A on each side of the breaker. The neutral in this case would carry no current, just as if the supply were from a xfmr.



Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7601 MB (Peak: 0.8931 MB) Zlib enabled. Server Time: 2017-07-28 06:54:35 UTC