#181382 - 10/06/08 12:08 PM Voltage problem  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 819
NC
I have a friend who called me over to check his garage voltage out. He had some 120 volt outlets not working. He has a 120/240 feeder coming from his house feeding underground to a garage about 75ft. away. I check the voltage and find out that there's one phase not getting the right voltage. I was getting 123 volts to ground on one phase, and around 74 volts on the other phase. At first I thought one of the conductors were broken or burned under ground, then I traced it down to a HID fixture mounted on the outside of his garage. When I turned this breaker off, the voltage came back to 245 volts between phases. I then hooked up everything the way it was before ( I had to change the piece of rusted conduit that was coming up into the panel. After I hooked it all back up, I checked the voltage again. It corrected the voltage almost, but I'm still getting 123 volts on one phase and only about 111 volts on the other phase. Still seems to be something not exactly right.First question is how would a bad ballast in the light make the power to fluctate on the main lugs like this? 2nd question: Do you think there still might be a "bad wire" under ground causing the difference in voltage on the two phases? Thanks for the input.. Steve


Work Gear for Electricians and the Trades

#181383 - 10/06/08 12:39 PM Re: Voltage problem [Re: sparkync]  
Sandro  Offline
Member
Joined: Dec 2001
Posts: 444
Stoney Creek, ON, Canada
Sounds to me like an underground problem. When there is no heavy load, likely you read "normal" voltage. When load is applied, then the probs manifest itself.



#181387 - 10/06/08 02:02 PM Re: Voltage problem [Re: Sandro]  
maintenanceguy  Offline
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
Yes, a bad wire. A bad neutral wire.

Since the neutral path back to the main panel is broken, you aren't drawing current from a hot wire and neutral. You are drawing current from the hot wire and all of the appliances, lights, stereos, etc on the other hot wire.

When the load is balanced perfectly between the two legs, the voltage will be balanced. Any imbalance in load will cause an imbalance in voltage.


#181429 - 10/07/08 05:07 PM Re: Voltage problem [Re: maintenanceguy]  
gunther  Offline
Member
Joined: Sep 2003
Posts: 60
I would check the neutral out, it's connection, and also the connections of the grounding electrode. I've seen a corroded attachment to a grounding rod cause some odd things, like getting 75 volts from the water running out of a faucet to a stainless steel sink or a guy's wife getting a shock by the water in her washer.


#181431 - 10/07/08 07:04 PM Re: Voltage problem [Re: gunther]  
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
111 volts on one leg is indicative of the failure being on that particular hot leg, not the neutral. It should be easy to determine by removing all loads and measuring between each leg to the neutral (NOT the ground).


---Ed---

"But the guy at Home Depot said it would work."

#181434 - 10/07/08 08:13 PM Re: Voltage problem [Re: EV607797]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Ed, what if it measures 111 on one leg, and 129 on the other?

(The neutral would be the suspect)

I agree with your method of removing the loads, it should read 120 on A, and 120 on B to the neutral conductor.

_________________________________________________________

Quote
He had some 120 volt outlets not working. He has a 120/240 feeder coming from his house feeding underground to a garage about 75ft. away.


If it's a separate structure, then it needs to comply with 250.32(A) in regard to having the required grounding electrode installed, and its connection.


#181439 - 10/07/08 10:28 PM Re: Voltage problem [Re: electure]  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 819
NC
Thanks for the replies. I haven't got a chance yet to go back and check the voltage again. It only has a 3 wire feeder to the panel in the garage. There was some digging in the near proximity of it a few months ago( 3 feet or so), but the owner hasn't said anything about any problems til now. I guess it's possible a wire got nicked somewhere, and is just now deteriorating to the point of causing a problem. We will just have to dig in the general area and see if that's the problem. I originally told him, it looked like a wire was broken underground, so we may still have that problem. Thanks again... Steve


#181441 - 10/07/08 10:44 PM Re: Voltage problem [Re: sparkync]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
You could disconnect the wire at both ends and loop a load through them in different combinations checking voltage drop across the link. Use something hefty like a space heater so the voltage drop was apparent.


Greg Fretwell

#181442 - 10/07/08 11:47 PM Re: Voltage problem [Re: gfretwell]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Did you check it back at the main? May not be the sub at all.



Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.8029 MB (Peak: 0.9716 MB) Zlib enabled. Server Time: 2017-05-25 23:52:06 UTC