#180811 - 09/11/08 04:11 PM Service Entrance Grounding  
thiggy  Offline
Member
Joined: May 2004
Posts: 24
B'ham Al
While examining my mother's fuse panel, I started wondering about the grounding system. Her house was built about 1960, and has a 100 amp fuse box on the inside basement wall, with a 100 amp cartridge fuse disconnect outside beside the meter. I noticed that the outside box has a bare ground wire which runs in to the fuse box, then up to the cold water copper tubing which runs above the fuse box. There is no ground rod driven into the soil. Is this an appropriate method of grounding the service panel? I wonder about the continuity of the copper plumbing, particularly where there is a pressure regulator in the line. Should this go to a ground rod in the soil rather than being clamped to the water system?


Work Gear for Electricians and the Trades

#180812 - 09/11/08 04:30 PM Re: Service Entrance Grounding [Re: thiggy]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,116
Estero,Fl,usa
Back when all water distribution was metal that was the best grounding electrode. The whole city was tied to the same equipotential grid. Now that everything is plastic that is no longer true so we have the requirement for the supplemental electrode. I would drive a rod and connect it to the panel. If there is any question about the conductivty of the pressure regulator (not all metal body) jumper around it.


Greg Fretwell


Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.024s Queries: 15 (0.003s) Memory: 0.7437 MB (Peak: 0.8620 MB) Zlib enabled. Server Time: 2017-09-23 05:48:21 UTC