Need Code Reference #180445
08/26/08 04:40 PM
08/26/08 04:40 PM
F
Fred  Offline OP
Member
Joined: Apr 2001
Posts: 449
Straughn, IN 47387
I have an inspector who says I cannot have a main breaker in a 200A panel mounted in a building addition fed from a 200A breaker in a 320A meter/main. Feeders are 3/0,3/0,3/0,#2 THHN/THWN copper underground in 2" PVC. The second 200A panel is located back-to-back with the meter/main and has a 200A main as well but he says that is okay. He maintains the panel in the addition must be MLO. I cannot find anything in the 2008 NEC to support his position. Any idea where he is getting this idea?

2017 / 2014 NEC & Related Books and Study Guides
Re: Need Code Reference [Re: Fred] #180450
08/26/08 06:16 PM
08/26/08 06:16 PM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
I'd ask HIM cite the particular code article, whether NEC or a local code addition. He cannot just say "no". He's obliged to provide you with this. No need to be rude about it since you are just asking the basis for his decision.

A cop can't pull you over and write you a ticket just because he feels like it either. They must also cite what you did wrong, by referencing the locally adopted code.

Has the '08 code even been adopted in your area yet?


---Ed---

"But the guy at Home Depot said it would work."
Re: Need Code Reference [Re: EV607797] #180453
08/26/08 07:14 PM
08/26/08 07:14 PM
F
Fred  Offline OP
Member
Joined: Apr 2001
Posts: 449
Straughn, IN 47387
Indiana adopted the 2008 NEC effective 7/16/08 but they still haven't published the ammendments. Rumor has it they deleted the AFCI requirement again and its expansion.

Re: Need Code Reference [Re: Fred] #180457
08/26/08 07:41 PM
08/26/08 07:41 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
The inspector might be referencing Article 408 Section 408.36 and miss applying it. In a nutshell you need overcurrent protection for a panelboard and the exception says that it's not needed if the feeder has protection sized to protect the panelboard. The '05 code say it's not required but I guess if you have it it's not a violation. the '08 changes it somewhat but the end result is the same.

That's like saying you need 4 receptacles in a wall space and you decide to install 6, that's not a violation.

There is no hazard with having properly sized feeder overcurrent protection feeding a panelboard and having the same size overcurrent device in the panelboard.

Sometimes a panel with a main is cheaper than a MLO.


George Little
Re: Need Code Reference [Re: George Little] #180506
08/28/08 10:39 AM
08/28/08 10:39 AM
S
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
A main breaker in this application is not required, but certainly not prohibited. In this case, the main breaker is not functioning as OCP, but merely as a local disconnect. It could even be larger than the 200A feeder breaker, and not be an issue.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Potseal 14
Popular Topics(Views)
243,554 Are you busy
180,361 Re: Forum
170,838 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.003s) Memory: 0.9672 MB (Peak: 1.1090 MB) Zlib enabled. Server Time: 2018-01-20 01:14:34 UTC