A.I.C. #18030
12/05/02 02:55 PM
12/05/02 02:55 PM
W
Wirenuttt  Offline OP
Member
Joined: Nov 2002
Posts: 267
Massachusetts
Lets say you're wiring a new school. Main electric room calls for a certain aic rating on all the main switch gear. Does this aic rating have to follow suit throughout the building, to all the sub panels and breakers?
Is there a code?

[This message has been edited by Wirenuttt (edited 12-05-2002).]

Work Gear for Electricians and the Trades
Re: A.I.C. #18031
12/05/02 04:30 PM
12/05/02 04:30 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Wouldn't this be a case where "series-rated" system design would come into play?
I'm sure an informative thread could be generated on the subject.

Re: A.I.C. #18032
12/05/02 04:41 PM
12/05/02 04:41 PM
G
Gwz  Offline
Member
Joined: Apr 2002
Posts: 197
Check 110.9, 110.10, 110.22 ( 2nd paragrpah ), 240.2 Current-Limiting OCP device, 240.83(C), 240.86.

Suggest you try the Bussmann site http://www.bussmann.com and look for their SPD download and their many other free software and bulletins.

Re: A.I.C. #18033
12/05/02 04:49 PM
12/05/02 04:49 PM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
The AIC rating of breakers in downstream subpanels and the bracing of the busbars in these panels can probably be lower than what is required at the main. Inductive reactance will lower the available fault current.

Hopefully, the engineer did the analysis ahead of time.

If you want to play around with some short circuit calculations, visit the following site for free software downloads http://www.bussmann.com/apen/software/


Few things are harder to put up with than the annoyance of a good example.
Re: A.I.C. #18034
12/05/02 05:05 PM
12/05/02 05:05 PM
E
electric-ed  Offline
Member
Joined: Jul 2002
Posts: 175
Canada
The use of current-limiting fuses in the main service disconnecting means can also limit the available fault current downstream.

Ed

Re: A.I.C. #18035
12/05/02 07:38 PM
12/05/02 07:38 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Current limiting fuses do not reduce the short circuit available at down stream equipment. They will limit energy for flash protection calculations, but not fault current for AIC or withstand ratings. The up-over-down method of determining let-through from the fuse curve as been found to be inaccurate due to "dynamic impedance" with downstream overcurrent protection. Similar reasons with a listed series combination between fuse and downstream breaker must be tested before it can be considered series rated.


Ron
Re: A.I.C. #18036
12/05/02 07:44 PM
12/05/02 07:44 PM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
From the Bussman.com website: http://www.bussmann.com/library/techspec/TechSpec12.pdf
Up-Over-Down Method:
With series rated combinations, the up-over-down method is not able to be used to determine the protection of newer
style circuit breakers with blow-apart contacts (which exhibit dynamic impedance). For these applications, listed
equipment which has been labeled for use with tested combinations must be installed. Despite the inability to predict
protection for circuit breakers using the up-over-down method, the method is still (as it always has been) valid for
static components (components passive within first half-cycle). Some applications which can utilize the up-overdown
method include:
1. Bus-Bracing Requirements
2. Wire and Cable Protection

Poster's note: It appears that a portion of equipment withstand ratings can use this chart method.


Ron

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,587 Are you busy
180,382 Re: Forum
170,859 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.9839 MB (Peak: 1.1366 MB) Zlib enabled. Server Time: 2018-01-22 02:18:48 UTC