ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Recent Posts
VFD MotorFeeders
by gfretwell. 10/19/17 01:02 AM
Generator Cable Sizing
by brsele. 10/18/17 07:39 PM
What do you do?
by gfretwell. 10/17/17 01:08 AM
Good ol' copper pipe in the fuse holder trick
by HotLine1. 10/16/17 07:16 PM
Another generator question
by HotLine1. 10/16/17 07:02 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
241,443 Are you busy
177,420 Re: Forum
169,010 Need opinion
Who's Online Now
0 registered members (), 10 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#180169 - 08/15/08 04:52 PM Insta-Hot breakers  
wiking  Offline
Junior Member
Joined: Dec 2002
Posts: 32
Florida, USA
For years I have always up sized the breaker by at least 125% of the load on an Insta-Hot (sometimes known as a Tankless Water Heater). Now I find out that since it is considered a non-continuous load, I can size the breaker according to the load, at least according to one supplier and a company tech rep I talked to.
This would have made things much easier if I had known this, but am glad I know now.
Doesn't it seem to be pushing it too close to have the breaker right at the amp load? What about nuisance tripping in case of a weaker or eventually worn breaker?
Factor in things like voltage drop or perhaps the device slightly raising it's ampacity over time due to wear or tear, it seems like a potential for at least some minor problems.
Another question I have is whether a disconnect is required under the sink with the Insta-Hot. A well respected (and feared by some) inspector told me that if there was not a requirement on the blueprint for a disconnect, it doesn't need one according to code. I definitely always label the breaker in the panel and write on the insta hot what circuit and panel it is.


2017 / 2014 NEC & Related Books and Study Guides

#180184 - 08/16/08 08:13 AM Re: Insta-Hot breakers [Re: wiking]  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Your supplier & tech rep are correct about circuit sizing. See 422.10

The circuit breaker can sevre as the disconnecting means but will probably need a provision for attaching a padlock and the provision must remain in place with or without the padlock. 422.31(B)


Few things are harder to put up with than the annoyance of a good example.

#180196 - 08/16/08 12:35 PM Re: Insta-Hot breakers [Re: Tom]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,123
Estero,Fl,usa
Around here they will usually want the local disconnect. Our AHJs do not think much of residential LOTO capabilities. Up to 20a this is usually cord and plug, 25a and up is going to be a pullout or switching device.


Greg Fretwell


Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.002s) Memory: 0.7526 MB (Peak: 0.8756 MB) Zlib enabled. Server Time: 2017-10-22 10:01:39 UTC