#180090 - 08/12/08 09:47 PM A Problem With Low Tide And Conduit Runs  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,450
NY, USA
Quote
I found this in Tacoma, WA at a harbor were my Aunt and Uncle's sailing vessel is moored

The flexible conduit wasn't long enough to accommodate the lengths at the low tide levels so the conduit connections came apart

Tristan S.

[Linked Image]

[Linked Image]


2017 / 2014 NEC & Related Books and Study Guides

#180091 - 08/12/08 09:48 PM Re: A Problem With Low Tide And Conduit Runs [Re: Admin]  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,450
NY, USA
Quote
Here's another one I found at the same harbor in Tacoma, WA but on a different dock access ramp.

I don't know what kind of tubing was used to take the place of flexible conduit here but I certain it's not LFNC or any other code approved conduit.

It almost looks like a vacuum hose but I'm not sure.

Tristan S.

[Linked Image]


#180095 - 08/13/08 12:36 AM Re: A Problem With Low Tide And Conduit Runs [Re: Admin]  
packrat56  Offline
Member
Joined: Mar 2008
Posts: 76
MT, U.S.
One thing I forgot to mention about the top two pictures is the PVC conduits seen there are supported by the dock access ramp I was on at that time.


I have a sense of adventure, I just keep it leashed with common sense.

#180166 - 08/15/08 04:06 PM Re: A Problem With Low Tide And Conduit Runs [Re: packrat56]  
jdevlin  Offline
Member
Joined: Aug 2002
Posts: 402
welland ontario canada
Looks like they used the wrong glue on the PVC as well. They connections should not come apart like the bottom picture. They should break.


#180168 - 08/15/08 04:44 PM Re: A Problem With Low Tide And Conduit Runs [Re: jdevlin]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,260
Fullerton, CA USA
Originally Posted by jdevlin
Looks like they used the wrong glue on the PVC as well. They connections should not come apart like the bottom picture. They should break.


Not if the connections were glued wet, at high tide. smile



#180178 - 08/15/08 09:41 PM Re: A Problem With Low Tide And Conduit Runs [Re: electure]  
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
I've seen a few joints come apart like that, including one that I put in myself (and I was using the conduit manufacturer's glue!). The problem does seem to have something to do with marine environments.

I've taken to using a clear PVC primer on the pipe and fittings before applying the cement, just like you would on plumbing work. It definitely seems to result in a stronger joint...



#180188 - 08/16/08 10:13 AM Re: A Problem With Low Tide And Conduit Runs [Re: NJwirenut]  
NORCAL  Offline
Member
Joined: Sep 2002
Posts: 872
Originally Posted by NJwirenut
I've seen a few joints come apart like that, including one that I put in myself (and I was using the conduit manufacturer's glue!). The problem does seem to have something to do with marine environments.

I've taken to using a clear PVC primer on the pipe and fittings before applying the cement, just like you would on plumbing work. It definitely seems to result in a stronger joint...



Clear PVC primer? Do you have any info on it? Purple primer is quite ugly.


#180193 - 08/16/08 11:26 AM Re: A Problem With Low Tide And Conduit Runs [Re: NORCAL]  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
He might actually be using an even thinner product, sold as a 'cleaning' compound. I have seen clear primer, though ... sometimes at the home centers!

The joint in the picture appears to have used a gray cement, which I have seen sold in the plumbing aisle. The stuff I've seen that was actually listed for electrical use has always been clear. The clear glue is definitely thinner than the plumbing cements.

I will admit to changing my practices according to the conditions of the job site. For example, the listed cement is a poor choice in the summer sun - it dries too fast for you to make up your connections - while it works quite well in cooler temps.

Since we do not usually use a primer, I have also found it necessary to apply the glue to both halves of the connection. I think you really need the solvent to have some time to 'open up' the pipe surfaces before you can expect the cement to 'weld' them together.

Not that electricians pay much attention to PVC joints ... it's not like we're worried about electricity leaking out under pressure laugh


#180194 - 08/16/08 12:14 PM Re: A Problem With Low Tide And Conduit Runs [Re: renosteinke]  
NJwirenut  Offline
Member
Joined: Sep 2001
Posts: 806
Bergen County, NJ
The glue sold by at least 2 PVC conduit manufacturers (Carlon and Cantex) is a heavy-bodied grey cement. That's the stuff I generally use.

The clear primer I have used is manufactured by Oatey, sold in the plumbing aisle of the orange box stores:

[Linked Image]

http://www.oatey.com/Plumber/Shared/ProductGroupDetail/174/Clear+Primer+%E2%80%93+NSF+Listed.html


Last edited by NJwirenut; 08/16/08 12:20 PM.

#180199 - 08/16/08 05:07 PM Re: A Problem With Low Tide And Conduit Runs [Re: NJwirenut]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,260
Fullerton, CA USA
Carlon PVC glue is manufactured by Oatey.

I'd bet that they're the same products, with different labeling.


Page 1 of 2 1 2

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 