Permanent wall penetration for temporary cables. #179726
07/29/08 11:38 AM
07/29/08 11:38 AM
L
LarryC  Offline OP
Member
Joined: Jul 2004
Posts: 783
Winchester, NH, US
What is the correct method to install a feed-thru thru a wall?

I am envisioning a 6" square box with a cover, on each side of the wall and 2 short pieces of 2" EMT connecting the two boxes.

The feed-thru would be used to run temporary power, communication cables, liquid lines, etc. Obviously the covers would be installed when the pass-thru is not in use.
One side of this feed-thru is in a conditioned space and the other side is the building's loading dock.

Thanks,

Larry C

Work Gear for Electricians and the Trades
Re: Permanent wall penetration for temporary cables. [Re: LarryC] #179743
07/29/08 07:32 PM
07/29/08 07:32 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 6,919
Brick, NJ USA
Larry:
Is it a fire-rated wall??
Condensation may also be an issue.


John
Re: Permanent wall penetration for temporary cables. [Re: LarryC] #179746
07/29/08 08:29 PM
07/29/08 08:29 PM
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
This is primarily a design issue, but a good one for discussion.

For a fire rated wall, the key is to restore / maintain the fire resistance of the wall. Even for a 'normal' wall, the idea is to keep noise, drafts, etc., from passing through.

The method you propose isn't bad ... though I would use 'running thread,' rather than trying to get nipples to to be the right size. I'm a bit puzzled as to why you would want two nipples though ... keep in mind that all conductors of a circuit need to be run in the same nipple, and that you need a partition between low voltage and power cables.

Easier to do, perhaps, is to install one of the commercially available fire-stop products. These are nicely made tubes, flanges on either side .... and large enough to pass your pipes through. You seal the remaining gaps with the appropriate products, and all is well.

How to make the necessary holes in the wall? A roto-hammer, with the appropriate core drill, makes easy work of the chore.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Popular Topics(Views)
243,607 Are you busy
180,424 Re: Forum
170,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.011s Queries: 15 (0.003s) Memory: 0.9509 MB (Peak: 1.0768 MB) Zlib enabled. Server Time: 2018-01-24 09:42:26 UTC