#178562 - 06/04/08 05:07 PM Pig Tailing AL to Copper  
dougwells  Offline


Member
Joined: May 2003
Posts: 1,138
kamloops BC Canada
I get many calls from customers thinking we can just pig tail copper onto aluminum with the proper # 63 marrette. I have always thought it was best to replace the devices with c0/alr devices but i havent seen these in Decora.


Tools for Electricians:

#178564 - 06/04/08 06:51 PM Re: Pig Tailing AL to Copper [Re: dougwells]  
Rewired  Offline
Member
Joined: Jan 2006
Posts: 558
Hamilton, Ontario, Canada
I dont think there is such an animal as a CO/ALR rated decora device..
A.D


#178593 - 06/05/08 11:54 PM Re: Pig Tailing AL to Copper [Re: Rewired]  
marsbar  Offline
Member
Joined: Apr 2006
Posts: 31
london, ont, canada
Yes I have some on order through Westburn Ruddy, they are purple, chemically treated and allow for different expansion rates or so the sales promo tells me. I thought the was a marrett with a copper tail that was allowed for AL wired homes. I have seen a few homes with AL/CU mixed and was looking for the best way (penetrox and an 833 with a piece of CU takes up space)to help these people out.


#178594 - 06/05/08 11:57 PM Re: Pig Tailing AL to Copper [Re: marsbar]  
marsbar  Offline
Member
Joined: Apr 2006
Posts: 31
london, ont, canada
Sorry, I should have read the question better and I have not seen a AL Decora device.


#178618 - 06/06/08 05:31 PM Re: Pig Tailing AL to Copper [Re: dougwells]  
u2slow  Offline
Member
Joined: Sep 2003
Posts: 200
Salt Spring, BC, Canada
Has anyone seen a Cu/AL pigtail (well-twisted and w/compound) go bad?

I'm curious because to me it seems like as good - or better - a connection than #12 AL wrapped on the screw terminal. Then you don't need to keep AL-rated devices in the truck.


#178628 - 06/06/08 10:53 PM Re: Pig Tailing AL to Copper [Re: u2slow]  
twh  Offline
Member
Joined: Mar 2004
Posts: 916
Regina, Sask.
I haven't seen many cu/al connections, at all. Has anyone seen a cu/al connection last for 10 or 20 years?


#178732 - 06/10/08 12:08 PM Re: Pig Tailing AL to Copper [Re: twh]  
marsbar  Offline
Member
Joined: Apr 2006
Posts: 31
london, ont, canada
Please correct me but isn't that the problem: 10-20 years of mixed metals causing corrosion and heat? I understand that Penetrox should be redone every 5 years (but they say the fixture should be replaced every 5 years)


#178736 - 06/10/08 03:55 PM Re: Pig Tailing AL to Copper [Re: twh]  
Hendrix  Offline
Junior Member
Joined: Jan 2007
Posts: 22
NH
what about split bolts?


#178738 - 06/10/08 04:31 PM Re: Pig Tailing AL to Copper [Re: Hendrix]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
I know the OP and most of the other posters in this thread are from the great white north, but wanted to chime in anyway.
Last year I switched to the connectors below after learning some unsavory info about those purple wirenuts.
These are listed for CU and AL wires. The only thing is that you will need to buy and use a torque-limiting screwdriver to install them for UL/CSA listing compliance. They can also fill up a device box quickly if you have several splices to make.
The company sent a free sample connector before I purchased in quantity.

Here is the product link. http://www.alcopstore.com/



#178739 - 06/10/08 05:18 PM Re: Pig Tailing AL to Copper [Re: KJay]  
dougwells  Offline


Member
Joined: May 2003
Posts: 1,138
kamloops BC Canada
Originally Posted by KJay
I know the OP and most of the other posters in this thread are from the great white north, but wanted to chime in anyway.
Last year I switched to the connectors below after learning some unsavory info about those purple wirenuts.
These are listed for CU and AL wires. The only thing is that you will need to buy and use a torque-limiting screwdriver to install them for UL/CSA listing compliance. They can also fill up a device box quickly if you have several splices to make.
The company sent a free sample connector before I purchased in quantity.

Here is the product link. http://www.alcopstore.com/



I got the sample also but i have not found a Canadian supplier for them yet

I have a stock of these i use for now.

http://www.tnb-canada.com/en/catalogues/online/comresconstruction/pdf/c5/09_marrcat_e.pdf


Page 1 of 2 1 2

Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 16 (0.003s) Memory: 0.8185 MB (Peak: 0.9985 MB) Zlib enabled. Server Time: 2017-07-23 12:34:46 UTC