New: 3 Phase 3 Wire ungrounded Delta DrawingsThese are new drawings as of 05/03/2008. Feel free to comment.The following drawings describe a 3 Phase 3 Wire Ungrounded Delta
Transformer connection, and the nominal Voltages at various points.
Drawings included are for 240V, 480V and 600V 3 Wire Deltas.
***NOTE: These systems are not "Physically" Grounded*** meaning a Low Impedance Circuit between any Line to Ground will draw very little Current - and the Voltage across that load will be very small - like 10 Volts across an Impedance of 100 Ohms.
HOWEVER!!! If measured across a High Impedance (Line to Ground), the Voltage to ground may at times exceed the Phase to Phase Voltage, by as much as 3 times the L-L Voltage - and possibly more!
What I am referring to here is measuring Voltage from Line to ground using a "Digital Volt Meter" - which typically have a very high input Impedance ( > 500K Ohm, possibly even 10Meg Ohm), will read a Voltage of 300 Volts and up.
Using a low Impedance meter - like an old "Wiggy" (Solenoid type Voltmeter), will display almost zero Volts when connected Line to Ground.
The same applies when fixed loads of low or high Impedance are connected L-G
Please take note of this issue (issue is due to "Capacitive Coupling Effect).
Now On To The Drawings!!!![[Linked Image]](https://www.electrical-contractor.net/theory/D3W_UNGRND_240_SCH_G.gif)
Figure 1a: Schematic drawing of the 240VAC
3 Phase 3 Wire Ungrounded Delta.
![[Linked Image]](https://www.electrical-contractor.net/theory/D3W_UNGRND_240_LAYOUT_G.gif)
Figure 1b: Layout drawing of the 240VAC
3 Phase 3 Wire Ungrounded Delta.
=========================================================================
=========================================================================
![[Linked Image]](https://www.electrical-contractor.net/theory/D3W_UNGRND_480_SCH_G.gif)
Figure 2a: Schematic drawing of the 480VAC
3 Phase 3 Wire Ungrounded Delta.
![[Linked Image]](https://www.electrical-contractor.net/theory/D3W_UNGRND_480_LAYOUT_G.gif)
Figure 2b: Layout drawing of the 480VAC
3 Phase 3 Wire Ungrounded Delta.
=======================================================================
=======================================================================
![[Linked Image]](https://www.electrical-contractor.net/theory/D3W_UNGRND_600_SCH_G.gif)
Figure 3a: Schematic drawing of the 600VAC
3 Phase 3 Wire Ungrounded Delta.
![[Linked Image]](https://www.electrical-contractor.net/theory/D3W_UNGRND_600_LAYOUT_G.gif)
Figure 3b: Layout drawing of the 600VAC
3 Phase 3 Wire Ungrounded Delta.
========================================================================