#177018 - 04/19/08 07:30 AM Xo on a dry type transformer  
Angel_Electric  Offline
Member
Joined: Jun 2007
Posts: 20
Fl.
I wired my first dry type transformer. My superior came to me afterwards and expressed that I needed to run a bonding jumper from the case of the transformer to Xo. The question I have is why is this important? 480v/208v-120v


Tools for Electricians:

#177020 - 04/19/08 08:26 AM Re: Xo on a dry type transformer [Re: Angel_Electric]  
WESTUPLACE  Offline
Member
Joined: Mar 2004
Posts: 251
Kingwood, TX USA
Ground reference. Secondary of the transformer needs a bonding jumper to give some reference to ground otherwise the voltage between ground and any other terminal could be anything from 0 to 208v


#177031 - 04/19/08 06:28 PM Re: Xo on a dry type transformer [Re: WESTUPLACE]  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Because your transformer is an SDS it requires that the neutral be bonded to a GEC on the secondary side. This can be done in the transformer or in the enclosure containing the first disconnect.


#177041 - 04/20/08 05:03 AM Re: Xo on a dry type transformer [Re: JBD]  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,708
Anaheim, CA. USA
Angel_Electric:

The Transformer's case needs to be bonded to "Both Sides", in case of a Ground Fault.
What I mean here is the case is bonded with the following:
  1. An Equipment Grounding Conductor brought in with the "Primary Feeders" (whatever Branch Circuit is feeding the Transformer),
  2. A System Bonding Jumper from the Grounded Conductor on the "Secondary Side" (whatever is leaving the Transformer - AKA: the Separately Derived System, or "SDS")


With the Bond described in "A" above, a Ground Fault from a "Primary Feeder" to the Transformer's case will have a low Impedance path, and (hopefully) trip the Over Current Protection Device (OCPD) on the Feeders for the Transformer.

With a solid Bond, such as described in "B" above, a Ground Fault from a "Secondary Feeder" to the Transformer's case will be able to (hopefully) load up the Primary Feeder's OCPD and eventually cause it to trip.

WITHOUT the Bonding described in "B" above, the Transformer's case may remain energised if a Ground Fault occured internally on a Secondary Feeder.

FYI: Even an Ungrounded System with Ungrounded SDS's will have Transformer cases bonded to a given Grounding Electrode System, plus connected to Equipment Grounding Conductors - only difference is there will be no Bonding Jumper between the SDS and the Grounded Equipment or Grounding Electrode System.

Here are a few Schematics for references:

================================================================
================================================================
[Linked Image]

Fig. 1: Single Phase Transformer - with 3 Wire Center Tapped Secondary.

Center Tapped Conductor is the Separately Derived System's Grounded Conductor.

=================================================================
=================================================================


[Linked Image]

Fig. 2: 3 Phase 4 Wire Wye Secondary - "X0" originates at the "Star Point" connection for all three Secondary Coils (Windings).

This "Star Point" is tapped, and the Conductor which is derived from the star point is the Common Neutral Conductor.
Grounding that tapped Conductor makes it the Separately Derived System's Grounded Conductor.

=======================================================================
=======================================================================

[Linked Image]

Fig. 3: 3 Phase 4 Wire Delta Secondary.

The Grounded Conductor is also a Center Tap, as described in "Fig.1" above.

=======================================================================

Hope this is helpful.

Scott


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

#177061 - 04/21/08 03:44 AM Re: Xo on a dry type transformer [Re: Scott35]  
Angel_Electric  Offline
Member
Joined: Jun 2007
Posts: 20
Fl.
You demystified the confusion. I Appreciate the pics. Also having seen yet another acronym spelled out has kept any further confusion from occurring. Thanx


#177066 - 04/21/08 06:02 AM Re: Xo on a dry type transformer [Re: Angel_Electric]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
Without the bonding jumper, the neutral is free to float, and though you may still see 120V phase-to-neutral on all phases, you might see one phase at 200V and another at 50V when you're expecting all to still be roughly 120V from ground. This tends to really mess with some equipment, especially surge supressors which are looking at voltage-to-ground and will discharge on the high leg.

The same is true of oil-filled transformers, as well; whenever there's a Y-secondary, you need to ground X0*.

* caveot for some generator/ATS setups, but that's getting a bit off track.




Member Spotlight
AllClear
AllClear
Belmond Iowa US
Posts: 44
Joined: August 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.7793 MB (Peak: 0.9267 MB) Zlib enabled. Server Time: 2017-11-24 12:55:20 UTC