ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 5
Recent Posts
Another generator question
by gfretwell. 09/21/17 02:41 PM
What do you do?
by gfretwell. 09/21/17 02:33 PM
Supporting conduit bodies
by ghost307. 09/18/17 12:12 PM
Thermal Imaging Camera upgrade
by Potseal. 09/18/17 11:57 AM
Linear Power Supply Quits Under Load
by JoeTestingEngr. 09/15/17 11:37 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,858 Are you busy
176,616 Re: Forum
168,529 Need opinion
Who's Online Now
0 registered members (), 49 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#176830 - 04/14/08 02:51 AM enclosure under sprinkler ?  
learner  Offline
New Member
Joined: Apr 2008
Posts: 3
BC Canada

Hi:

Base on CEC .

Does anybody know " What type enclosure box - 3R or 6P is right choice to used Under sprinkler " ?

Which rule?

thank you advance.

Leaner


Tools for Electricians:

#176864 - 04/14/08 11:18 PM Re: enclosure under sprinkler ? [Re: learner]  
Sixer  Offline
Member
Joined: Aug 2005
Posts: 265
Canada
Rule 26-008 and Appendix B
Is the enclosure in an electrical room or vault?


Sixer

"Will it be cheaper if I drill the holes for you?"

#176865 - 04/14/08 11:35 PM Re: enclosure under sprinkler ? [Re: Sixer]  
learner  Offline
New Member
Joined: Apr 2008
Posts: 3
BC Canada

Hi,sixer

Thank you.

the quiz not point out where is it.
from "Rule 26-008 and Appendix B" & table 65, I still can't make sure which type is right.

so could you please give more recommend?


#176880 - 04/15/08 08:52 AM Re: enclosure under sprinkler ? [Re: learner]  
Rick Kelly  Offline
Member
Joined: Jan 2006
Posts: 60
Iqaluit, NU, Canada
As per 2-400 and Table 65, type 4, or better, would be required.


#176892 - 04/15/08 01:00 PM Re: enclosure under sprinkler ? [Re: Rick Kelly]  
mikesh  Offline
Member
Joined: Jun 2006
Posts: 613
Victoria, BC, Canada
If the sprinkler is usually operating a type 4 is required. If it is for fire protection then any enclosure appropriate for the area without spriklers is ok. The normal use is what we determine the enclosure type not for a fire.

Now having said that there still are requirements for enclosures and equipment where a stream of water from a sprinkler head is required then 26-008 but that applies to the panels, transformers, switch boards etc.

A normal outlet box or JB where only wire and devices are installed would not require a special enclosure or every sprinled building would need to be completely wired per section 22.

In the case of a fire I presume we don't want the distrobution or transformers to fail from the sprikler putting water on the equipment. A fire pump or emergency lighting might be at stake. A wet location JB is overkill as this is a dry location except when a fire is present.


#177650 - 05/09/08 07:12 AM Re: enclosure under sprinkler ? [Re: mikesh]  
learner  Offline
New Member
Joined: Apr 2008
Posts: 3
BC Canada

Thank you all.
because It's a quiz. the answer is type 3R or 6P only.
base on R26-008. I choice 3R. is it right?




Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.019s Queries: 15 (0.003s) Memory: 0.7756 MB (Peak: 0.9250 MB) Zlib enabled. Server Time: 2017-09-22 08:00:45 UTC