ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 04/30/17 02:30 PM
201 volt equipment?
by bigpapa. 04/29/17 12:15 AM
Schneider LC1D09
by jraef. 04/28/17 11:05 PM
Electrode boilers question
by annemarie1. 04/27/17 01:40 PM
Why cables look like they do
by LongRunner. 04/26/17 09:36 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
235,042 Are you busy
169,884 Re: Forum
163,072 Need opinion
Who's Online Now
0 registered members (), 56 guests, and 9 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#176414 - 03/31/08 09:30 PM equipment ground/bond outside of conduit  
triple  Offline
Member
Joined: Apr 2002
Posts: 184
Wisconsin
Is an equipment ground/bond wire ever allowed to run along the outside of the conduit containing the feed wires for distances exceeding six feet (whether new or as a supplement to an existing installation)? BTW, replacing an ungrounded receptacle with a grounded one does not apply to this situation.

Thanks


2017 / 2014 NEC & Related Books and Study Guides

#176431 - 04/01/08 03:13 PM Re: equipment ground/bond outside of conduit [Re: triple]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
Bonding jumpers can only be max 6' 250.102(E)

... but see what you make of 250.120(C)

Quote
(C) Equipment Grounding Conductors Smaller Than 6 AWG. Equipment grounding conductors smaller than 6 AWG shall be protected from physical damage by a raceway or cable armor except where run in hollow spaces of walls or partitions, where not subject to physical damage, or where protected from physical damage.


... so you can run a ECG outside a raceway/cable if it is 6 or larger or otherwise protected from damage.

To be honest I have never seen it.


Greg Fretwell

#176432 - 04/01/08 03:36 PM Re: equipment ground/bond outside of conduit [Re: gfretwell]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,069
Estero,Fl,usa
I did see this discussed once in reference to adding grounds to a house that was ungrounded and it was surmised that you could run a bus of #6 through the crawlspace, attic or whatever was accessible and tap off #12 or #14 drops into the wall cavities to the boxes if the unprotected portion was very short, basically directly into the wall from the tap.

It seemed reasonable to me.


Greg Fretwell


Member Spotlight
Admin
Admin
NY, USA
Posts: 3,439
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 15 (0.003s) Memory: 0.7526 MB (Peak: 0.8770 MB) Zlib enabled. Server Time: 2017-05-01 04:28:10 UTC