#175044 - 02/20/08 02:09 PM Service Conductor size  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 834
Michigan
Total Load 3200 amps , Switch gear rated at 4000 amps

9 sets of 3-500 Kcmil & 1-4/0 neutral = 3420 amps.

Load 3200 Wire 3420 gear 4000 amps.

No main Six 800 amp switches

Legal per 230.80& 230.90 a EXCEPTION 3

READ PAGE 150 & 152 2005 NEC CODE HANDBOOK

Service Conductors Adquate for Load, Gear rated Above Load
Should be good to go Right.

Whatca say guys???
Yoopers


2017 / 2014 NEC & Related Books and Study Guides

#175045 - 02/20/08 04:40 PM Re: Service Conductor size [Re: Yoopersup]  
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Provided that your 3200 amp load is 125% of the continuous load plus 100% of the non-continuous load, I'd say OK.


Few things are harder to put up with than the annoyance of a good example.

#175046 - 02/20/08 05:50 PM Re: Service Conductor size [Re: Tom]  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 834
Michigan
That is the way it was Calculated.


#175057 - 02/21/08 11:13 AM Re: Service Conductor size [Re: Yoopersup]  
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
With six disconnects, and as calculated, it is Code compliant. Good to go. smile


Alan--
If it was easy, anyone could do it.


Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,431
Joined: February 2004
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 15 (0.003s) Memory: 0.7595 MB (Peak: 0.8934 MB) Zlib enabled. Server Time: 2017-11-18 21:14:09 UTC