#174261 - 01/30/08 07:24 PM Size of Equipment Grounding Conductors.  
Sparkman  Offline
New Member
Joined: Jan 2008
Posts: 1
North Carolina
Can anyone shed any light on 250.122(B)? Thank you in advance.


2017 / 2014 NEC & Related Books and Study Guides

#174265 - 01/30/08 08:25 PM Re: Size of Equipment Grounding Conductors. [Re: Sparkman]  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Sure, what do you want to know?


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#174283 - 01/31/08 02:48 AM Re: Size of Equipment Grounding Conductors. [Re: iwire]  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,124
Estero,Fl,usa
Short answer. If you upsize the conductors for something like voltage drop you also have to upsize the EGC.


Greg Fretwell

#174284 - 01/31/08 07:34 AM Re: Size of Equipment Grounding Conductors. [Re: gfretwell]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,213
Chesapeake, VA
They want to you increase the EGC by the same ratio you increase the current conductors. These #s are availible in Table 8

For example, lets say you have a 125A circuit (Normally #2 Cu w/#8 EGC) but have to increase the conductors to 1/0 to allow for derating:

#2 = 66kcmil
1/0 = 106kcmil
Increase is 60%.

#8 = 16.5kcmil.
16.5kcmil * 160% = 26.4kcmil

Looking through the table, #6 = 26.2kcmil, and would be the proper ground wire to use.


#174294 - 01/31/08 05:15 PM Re: Size of Equipment Grounding Conductors. [Re: SteveFehr]  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The interesting part is where you have a circuit protected at 30 amps or less....the EGC must be the same size as the circuit conductors. This often comes into play for parking lot lighting where you may be using a #4 or 6 on a 20 amp circuit.
Don


Don(resqcapt19)

#175836 - 03/12/08 02:09 PM Re: Size of Equipment Grounding Conductors. [Re: Sparkman]  
kohli  Offline
New Member
Joined: Mar 2008
Posts: 9
Ohlo Putnam Co
This is like many parts of the NEC which has been around from the early nightteen 30s when large pipe organ was popular

Now we have keyboardsand large amp systems or sound systems which make some of the old way of doing things of date , remember knob and tube, worked well in its day

Just food for thought thank you


#175838 - 03/12/08 02:54 PM Re: Size of Equipment Grounding Conductors. [Re: kohli]  
BPHgravity  Offline
Member
Joined: Apr 2003
Posts: 139
Port Charlotte, Florida
The conflict described by Don also occurs on equipment such as motors and air conditioning equipment that may have conductors that are permitted to be sized smaller than the branch circuit overcurrent device.

In many cases, the contractor will install conductors sized based on the max overcurrent device instead of the minimum branch circuit size and NOT increase the EGC in proportion.

The contractor doesn't understand why the EGC has to be increase when a smaller EGC is normally permitted for that circuit rating.

There were a couple proposals submitted this past code cycle that tried to clear up this issue, but none were accepted.

I have tried to come up with a good rewrite of 250.122(B) myself without much luck.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter


Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.019s Queries: 15 (0.004s) Memory: 0.7851 MB (Peak: 0.9419 MB) Zlib enabled. Server Time: 2017-10-22 20:57:13 UTC