ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
Dimmable LED 2x4 lay in fixtures
by Potseal. 04/23/17 07:18 PM
Old decora style outlets
by Lostazhell. 04/22/17 07:59 PM
Permit Snafus...AHJs and Contractors Jump in
by gfretwell. 04/22/17 01:11 PM
How do you find a good employee?
by HotLine1. 04/22/17 10:44 AM
Electrode boilers question
by SteveFehr. 04/21/17 08:32 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
234,650 Are you busy
169,334 Re: Forum
162,672 Need opinion
Who's Online Now
0 registered members (), 86 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#174187 - 01/28/08 07:02 PM Welder receptacle rating  
ole_electric  Offline
New Member
Joined: Sep 2007
Posts: 3
Metrowest Boston
Greetings everyone,

1st post for me here. I am installing a arc welder which calls for in it's litature using art. NEC 630-11 a OCPD @ 150 amps and conductor @ #4 (95 amps @ 90c table 310.16). The welder is single phase with a # 6 cord and a 50 amp plug. I ran the #4, but put in only a 50 amp OCPD backing up the 50 amp cord non fused disc. Duty cycle is 60%

My questions;
Why do they use 90 c column, most OCPD's and devices are 75c?
Should I have replaced the factory cord with 100 amp and direct wire with a disconnect or sell the cust a 100 amp cord, plug and recept.? OR just slap in a 150 amp backing the 50 amp recept! What if a different piece of equip is plugged in that location.

Many thanks guys!


2017 / 2014 NEC & Related Books and Study Guides

#174194 - 01/28/08 11:45 PM Re: Welder receptacle rating [Re: ole_electric]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,317
Alaska
The little extra amperage you can use for derating purposes like for wire count in conduits and ambient temperture corrections.

Welders wired under provisions of Article 630 Cord can use derate wire sized based on its duty cycle. The thought is with a 60% duty cycle meaning it is not to ran no more the 36 minutes per hour(60% of an hour). Even if the welder is cranking out 100 amps which will be rare with you welder if properly sized for the work, the cord will not get hot enough to cause damage. Besides the cord is part of the equipment which is not covered by the NEC. The outlet though is a different story. In theory, some other piece of equipment could be pluged in the the receptacle. The circuit must be able to carry the load.

The welder should be wired per the maufacuter's instuction. Failure to do so can void warranty and listing. If you void the listing, you can not use it. NEC requires all electrical components be listed or approved by a third party tester facility such as UL. That is why you see the little stamp like on a 4" square blank cover. Although it is just a square piece of metal, it still must be listed.


"Live Awesome!" - Kevin Carosa

#174197 - 01/28/08 11:55 PM Re: Welder receptacle rating [Re: sparkyinak]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Ole_electric, Welcome, you'll enjoy it here.


#174210 - 01/29/08 08:20 AM Re: Welder receptacle rating [Re: leland]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,205
Chesapeake, VA
Flexible cables for cords use table 400.5(B). #6-2 90°C Type W is rated for 99 Amps.

Personally, if it's cord-and-plug, I'd size OCPD for the cable & plug, too, regardless of what 630 says, because *anything* could be plugged into that receptacle. The breaker is designed to mimic cable heating, so (in theory) it shouldn't trip prematurely if the welder's duty cycle is OK for a 50A plug, even if current exceeds 50A.


#174211 - 01/29/08 11:22 AM Re: Welder receptacle rating [Re: SteveFehr]  
ole_electric  Offline
New Member
Joined: Sep 2007
Posts: 3
Metrowest Boston
thanks for your thoughts guys. I knew I came to the right place.

Right now I have a 50 amp OCPD, and watching how she does with the work. I'm not comfortable going up in size with the OCPD unless I change out the receptacle and plug to maybe just a disc. I know we size motor discs, plugs and recept's and to FLA and HP. That's EZ. Perhaps I'll call the mfg. I know we upsize OCPD for inrush on a still rotor with a motor. I'm wondering how the welder does on initial amps with that 50.


#174214 - 01/29/08 12:32 PM Re: Welder receptacle rating [Re: ole_electric]  
sparkyinak  Offline
Member
Joined: Jul 2007
Posts: 1,317
Alaska
Exstremely long day yesterday. Looked at one one message, yours. Welcome to the board.


"Live Awesome!" - Kevin Carosa


Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 216
Joined: March 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.020s Queries: 15 (0.003s) Memory: 0.7758 MB (Peak: 0.9246 MB) Zlib enabled. Server Time: 2017-04-24 15:18:01 UTC