#173483 - 01/10/08 08:20 PM Panel Cover Required where is nec 2005  
sokoservices  Offline
Member
Joined: Jan 2008
Posts: 22
Virginia
Hello All. I am new to this forum.

Where can I find in the 2005 code where it talks about the requirement for a panel cover? Where does it say that it is required. I can find pull boxes, j boxes, conduit bodies. etc. but I cant find it for panel boards.


Work Gear for Electricians and the Trades

#173488 - 01/10/08 08:51 PM Re: Panel Cover Required where is nec 2005 [Re: sokoservices]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
408.38 and 110.3(B),Then see ART. 100,Dead fronts.

This will determine if you need a cover.



#173489 - 01/10/08 08:55 PM Re: Panel Cover Required where is nec 2005 [Re: leland]  
sokoservices  Offline
Member
Joined: Jan 2008
Posts: 22
Virginia
Leland,
Here is the question, that is in question. Does 408.38 imply that a panel cover is required where there is live parts accessible to unqualified persons.


Virginia Journeyman Eletrician
NFPA-70E Trained
CFC Universal Certified

#173491 - 01/10/08 09:26 PM Re: Panel Cover Required where is nec 2005 [Re: sokoservices]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
sokoservices,
240.30 [A], requires the overcurrent devices to be protected from physical damage. 110.3[B] could also apply.


#173493 - 01/10/08 10:00 PM Re: Panel Cover Required where is nec 2005 [Re: sokoservices]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Originally Posted by sokoservices
Leland,
Here is the question, that is in question. Does 408.38 imply that a panel cover is required where there is live parts accessible to unqualified persons.



no. it states: "Panelboards shall be mounted
in cabinets,cutout boxes,or enclosures designed for the purpose and shall be dead front"

100-is deadfront...Why the heck am I transcribing the code for you? Go to the NFPA web site. They have a great version there. see for yourself.The live parts must be protected.

Any way, resi panels, usualy the deadfront is the cover. So whats the "real" question?

BTW, Welcome to the forums, you'll enjoy it here.
Get the book and learn your way around it.We are more than happy to help along the way.


#173494 - 01/10/08 10:15 PM Re: Panel Cover Required where is nec 2005 [Re: leland]  
sokoservices  Offline
Member
Joined: Jan 2008
Posts: 22
Virginia
Plain and simple.. Where in the code does it say I have to have panel covers on?

For example for boxes:
314.25 Covers and Canopies
In complete installations, each box shall have a cover, faceplate, lampholder, or luminaire (fixture) canopy, except where the installation complies with 410.14 (b)


What reference says for Electrical Panels?
I would say 408.38 then. Dead Front = Cover.

Thank you very much I have a code book. And i know how to use it. Its a matter of interpretation sometimes.


Virginia Journeyman Eletrician
NFPA-70E Trained
CFC Universal Certified

#173495 - 01/10/08 10:26 PM Re: Panel Cover Required where is nec 2005 [Re: sokoservices]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Don't take offence, no harm meant.
Your profile was slim so I have no idea of your level in the trade. Sorry.

408 is for panel boards, not boxes.
definition for deadfront says to cover live parts.
so if you have a deadfront your coverd. if not you need a cover to protect from live parts.

So I interpret that to read: put the panel board in an enclosure and install a deadfront to protect the(people) from live parts. Unless the mfgr. says to install a cover aswell,then thats what I do.


#173497 - 01/10/08 10:55 PM Re: Panel Cover Required where is nec 2005 [Re: sokoservices]  
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
I'm with you Sokoservices. This is yet another of those questions that's hard to answer. As long as I've been in this business, I've always heard the age-old adage that for every requirement in the NEC, there is an exception to that same requirement somewhere. Of course, the acronym "AHJ" is the true wild card that can literally shred your code book into packing material.

Technically, a residential panel today is "dead front" when you think about it if it's full of breakers. OK.......maybe the main lugs might be a questionable area. I can tell you that in my case, I would have to get into my GE panel with a coat hanger to get in trouble. Even with the cover off, all lugs are protected from accidental contact. If I wanted to touch the lugs of my main breaker, I would have to seriously grease my pinkie finger and force it into the hole where the hex wrench is inserted to tighten the lug.

I agree that it's not formally stated, but assumed to be "code" to have a panel cover in place. It's mostly about the manufacturer's approval. Perhaps their panel isn't approved or listed for use without the cover in place. You have to admit that this is the case with plenty of electrical equipment.

I can hang an 8', two light fluorescent strip without the covers. It will still work and there really won't be any additional live parts exposed. Still, this practice is wrong since the fixture assembly isn't complete per the approved listing without the covers in place.

Fear not: There are plenty of folks here who will jump in and try to help further with much better information than mine. Just give it a little bit of time. I learn something new here every day. You will too.


---Ed---

"But the guy at Home Depot said it would work."

#173515 - 01/11/08 12:47 PM Re: Panel Cover Required where is nec 2005 [Re: EV607797]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
This could probably go on forever, depending on your point of view, but here is my take on this.
I think the reason you don’t find an outright requirement in the NEC itself is because of the way the NEC defines a panelboard in Article 100. Using this component definition, the panel boards themselves would not be required to have a cover, especially when accessible only to qualified persons.
However, the "enclosure" that the panelboard is mounted in is designed in compliance with various standards, such as those in NEMA standards Publication 250 and NEMA standards Publication PB-2006, ANSI/UL 50, UL 589, and I'm sure, probably several others if we dig deep enough.
If I were the inspector on that job, I don’t think it would be a stretch to argue that if panelboard itself is listed and designed to be factory or field mounted in a NEMA rated "enclosure", then it must be listed as an equipment assembly, and that the listing for the equipment assembly with the NEMA rated "enclosure" includes a cover, regardless of whether or not the location is accessible to only qualified persons, since it is not possible to achieve even a NEMA 1 rating without a covered "enclosure".
I would probably site 110.2, 110.3[A], 110.3[B] before even downing my first morning cup of coffee, but that's just me. grin


#173520 - 01/11/08 05:11 PM Re: Panel Cover Required where is nec 2005 [Re: sokoservices]  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
Originally Posted by sokoservices
Hello All. I am new to this forum.

Where can I find in the 2005 code where it talks about the requirement for a panel cover? Where does it say that it is required. I can find pull boxes, j boxes, conduit bodies. etc. but I cant find it for panel boards.


A dead front, cover over the live parts, is part of the panel assembly so a corretly installed panel will include one.

However a cover with a hinged door, over the breakers, is not a requirement of any code or standard unless the enclosure is for special environments, like outdoors.

Last edited by JBD; 01/11/08 05:11 PM.


Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.032s Queries: 15 (0.011s) Memory: 0.8131 MB (Peak: 0.9945 MB) Zlib enabled. Server Time: 2017-09-26 12:40:09 UTC