Terminating Stranded Wire #172953
12/30/07 08:49 PM
12/30/07 08:49 PM
K
KJay  Offline OP
Member
Joined: Nov 2007
Posts: 763
MA, USA
What do you use to terminate small gauge stranded THHN wire on circuit breakers and devices?
I usually use the T&B Sta-Kons or 3M Highland crimp terminals but have also tried those Ideal Terminuts in the past.
Just want to see what method others are using and if maybe there is something different available.

TKX

Work Gear for Electricians and the Trades
Re: Terminating Stranded Wire [Re: KJay] #172954
12/30/07 08:54 PM
12/30/07 08:54 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
Devices and breakers are listed to accept stranded 12 and 14ga THHN


Greg Fretwell
Re: Terminating Stranded Wire [Re: gfretwell] #172959
12/30/07 09:50 PM
12/30/07 09:50 PM
L
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Clamps: Nothing.
T&B if I need a good (any) termination on a screw.

I'm so paranoid that even with solid, I wrap the screw. Those pressure connections seem to loosen up as I twist in the device.

K-J!! 16&0 Whata Ya think!!!!

Re: Terminating Stranded Wire [Re: gfretwell] #172960
12/30/07 09:53 PM
12/30/07 09:53 PM
B
BryanInBalt  Offline
Member
Joined: May 2007
Posts: 47
Baltimore
when I am forced to pull stranded to a device and the job doesn't spec the clamp type devices... I'll use some solid when I make up the box.

I've never had to connect smaller than 12 stranded to a breaker (which will work ok).


Design-Build isn't supposed to mean design *as* you build.
Re: Terminating Stranded Wire [Re: BryanInBalt] #172968
12/31/07 01:13 AM
12/31/07 01:13 AM
Theelectrikid  Offline
Member
Joined: Apr 2004
Posts: 810
Levittown, PA
I found it helps to twist the wire counter clockwise before making the hook with stranded.

In fact, I think I learned that here on ECN from a "tips" thread. Best bit of advice I've ever found here, sure helps with my traffic lights.

Ian A.


Is there anyone on board who knows how to fly a plane?
Re: Terminating Stranded Wire [Re: Theelectrikid] #172971
12/31/07 01:42 AM
12/31/07 01:42 AM
E
EV607797  Offline
Member
Joined: Oct 2006
Posts: 745
Fredericksburg, VA, USA
Same here. If I must terminate a stranded conductor on a screw terminal, I grab the end of the wire and twist it so tight that it almost handles like a solid conductor.

Simply stripping a stranded conductor and wrapping it messes up the natural lay of the strands and once you tighten the screw down, you end up mashing them down. Strands end up being left out of the termination. I don't like it.

In a perfect world, I'd use T&B Sta-Kons for all stranded to screw-terminal connections but that's another story.


---Ed---

"But the guy at Home Depot said it would work."
Re: Terminating Stranded Wire [Re: EV607797] #172983
12/31/07 06:04 AM
12/31/07 06:04 AM
J
jdo1942  Offline
Junior Member
Joined: Nov 2005
Posts: 31
st. louis, mo. usa
Most of us do not realize that most devices, outlets and switches are NOT rated for stranded wire. Read the listing on the box and you'll be using solid pigtails.

Re: Terminating Stranded Wire [Re: jdo1942] #172984
12/31/07 06:07 AM
12/31/07 06:07 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Originally Posted by jdo1942
Most of us do not realize that most devices, outlets and switches are NOT rated for stranded wire. Read the listing on the box and you'll be using solid pigtails.


The screw terminals of all UL listed 15 and 20 amp devices are listed for both stranded and solid building wire.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Terminating Stranded Wire [Re: iwire] #172986
12/31/07 08:07 AM
12/31/07 08:07 AM
K
KJay  Offline OP
Member
Joined: Nov 2007
Posts: 763
MA, USA
I seems that everyone does pretty much the same thing.
It’s true that device screw terminals are listed for stranded wire as well, but it’s sometimes a pain to wrap the wires neatly without loose strands, especially on the screw terminals of less expensive commercial spec grade and resi grade receptacles.
I will sometimes twist and then loop the stranded wire around the screw terminal as if I were looping to second device and then, after tightening, snip it off about 3/16” beyond the screw so the little piece of remaining insulation holds the strands together neatly.
However, many times in order to make things easier and to follow the UL 508a standard, I, like many other electricians, will use other approved means for terminating stranded wires as well.

UL508a Standard
A connection to a wire-binding screw shall be made as follows such that no loose strands protrude from the connection.
a) Solid wire formed into a loop at least three quarters (270 degrees) around the terminal, or
b) Stranded wire that is:
1) Soldered.
2) Connected to a terminal provided with upturned ends.
3) Connected to a terminal provided with a cup washer, or
4) Connected to a crimped pressure terminal connector or eyelet.

On circuit breakers, I personally don’t like connecting stranded conductors smaller than #10.
I’ve seen too many problems with heating and corrosion between strands with the squashing and separation that occurs with the clamp type terminals, like on SQD QO. The brands like Siemens that have a plain screw terminal seem to be worse by sometimes letting loose strands ride out the side of the screw when tightened.

JMHO

Re: Terminating Stranded Wire [Re: KJay] #173008
12/31/07 12:22 PM
12/31/07 12:22 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
From the UL Guide for Receptacles for Plugs and Attachment Plugs.
Quote
Terminals of the wire-binding screw, setscrew, or screw-actuated back wired clamping types are suitable for use with both solid and stranded building wires.


Don(resqcapt19)
Page 1 of 4 1 2 3 4

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,547 Are you busy
180,357 Re: Forum
170,836 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 16 (0.004s) Memory: 1.0283 MB (Peak: 1.2097 MB) Zlib enabled. Server Time: 2018-01-19 13:13:37 UTC